Do main bonding conductors have to be upgraded to 10mm when changing a consumer unit, my own opinion is as long as i am not adding any additional circuits or extending circuits i can leave 6mm as long as theres no signs of thermal damage, this would be just noted down as deviation on electrical cert, or on the other hand if i am changing cu then installstion has to comply with 17th edition, what does every one else think
 
I'd always check that the current bonding is adequate. If the main earth conductor is (and more importantly needs to be) 16mm then the bonding conductor SHOULD be at least half this....so 10mm is the one. I'd only not change it if I had a compelling reason not to, after confirming that the 6mm is adequate, of course!

You don't mention the earthing arrangement so can't be more specific.
 
I agree if its a tn-s earthing system and has 16mm earth then yeh the bonding conductor no less than half, but if its tnc-s then minimum on domestic will be 10mm.
 
On a Tn-s system, if you do the adibiatic equation and it works out you only need say 9mm main earth, then, even if you fit a 16mm main earth, you can leave 6mm bonding in place if there no sign of thermal damage. The bonding conductor should be not less than half the calculated main earth, and not half the size of the main earth thats fitted.

Saying that, I will always try and upgrade the bonding to 10mm wherever possible.

Jay
 
I'm confused.
The OP is obviously aware that the minimum CSA for bonding conductors where the system is TN-S is 6mm.
Why are they then asking whether the conductors have to be upgraded to 10mm?

You would only contemplate upgrading bonding conductors, if they did not satisfy the requirements of the Regulations.
As for noting down that the existing bonding conductors satisfy the Regulations as some sort of deviation, what's that all about?
 
Yes abit of self doubt, was kinda under the impression if you do work on domestic install you have to make sure it complies with 17th edition, ie if i install circuit buried in plaster it would have to be rcd protected. So i was thinkin same rule applies for change of consumer but if all is adequate ie 16mm tails protected by 60a fuse, they wont neccessary need replacing for 25mm which is only a recommendation so yes abit of self doubt as there is soooo many regulations with different opinions, i dont yet know what the system is but just a quick question how do you confirm that the csa of main bonding conductors are adequate enough.
 

Reply to 10mm bonding to water and gas in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
521
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
2K

Similar threads

In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...
Replies
11
Views
2K
  • Question
There could also be a completely unsuitable junction box embedded within the wall and tiled over or just cables in choc blocks in old accessory...
Replies
6
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top