Morning Chaps,

Can I clarify something please

Doing a job today have verified main bonding to water already but its only 6MM.
Does this have to be upgraded to 10mm when carrying out any works i.e CU change.

Even if continuity is checked and acceptable???

G
 
Think you will find that BRB says yes upgrade however if all is acceptable no need. We had a thread on this not so long ago and comment was passed about a question on niceic site that stated it was acceptable providing readings were correct.

Clear as mud as usual hope it helps


Chris
 
That depends on various things,

Earthing arrangement, t-n-c-s, t-n-s or t-t
Then if t-n-c-s 10mm minimum.
If t-n-s it must be at least 1/2 the size of your required main earth size.
 
Last edited:
For a PME system the csa of the main bonding conductors must not be less than that given in Table 54.8 ie a 10mm protective bonding conductor for a neutral conductor of 35mm or less. 544.1.1
 
Best answer mate no one can fault you for putting 10mm in many people would have a pop if you left it at 6mm so you have done what I always recommend cover YOUR back.


Chris
 

Reply to 10mm bonding in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
223
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
683
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
625

Similar threads

  • Question
Any metalwork connected to the MET could rise in voltage compared to true earth under an open supply neutral fault (on TN-C-S), and that would...
2
Replies
24
Views
2K
In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top