Stormflex

Changed CCU in my house and am completing the paperwork.

It appears that the earthing conductor is only 10mm. The main protective bonding conductors are also 10mm.

Am I obliged to upgrade this (will be no easy task!) or can I put this in the comments section on Form 1 and in the Deviations from Wiring Regulations box on the schedule of test results?
 
10mm for main bonding is fine. what's the problem getting a 16mm from the CU to the MET.? that's all you need.
 
I would point you to reg 131.8 in BS 7671.

You could then use the adiabatic equation to check wether the existing 10mm is sufficient, precluding a TN-C-S earthing system of course where is must be sized in accordance with the supply neutral conductor.
 
ok - looks like i'll have to go and buy some 16mm earth cable then.

telectrix - it'll just be a pig to route. CCU is in the top of a kitchen cupboard, MET is below worktop height right in the back corner of a cupboard on the wall at 90deg to CCU wall. They've basically wired it all up and then built the kitchen infront/around it. Just trying to get the end of the cable into the MET will be a challenge:

[ElectriciansForums.net] 10mm earthing conductor

But, I am sure I will overcome :D
 
ok - looks like i'll have to go and buy some 16mm earth cable then.

telectrix - it'll just be a pig to route. CCU is in the top of a kitchen cupboard, MET is below worktop height right in the back corner of a cupboard on the wall at 90deg to CCU wall. They've basically wired it all up and then built the kitchen infront/around it. Just trying to get the end of the cable into the MET will be a challenge:

View attachment 3510

But, I am sure I will overcome :D

You'll do that easy looks like a pain but once you get cracking it'll be a breeze.
 
Last edited by a moderator:
if the 10mm main earth is behind cupboards, maybe you can use it as a drag to pull the 16mm thru. good bit of practice for you here, sort of thing we have to do a lot of, or try a fish tape or rod alongside the tails. remember, for every problem there is another one round the corner.
 
Last edited:

Reply to 10mm earthing conductor in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
521
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
2K

Similar threads

Indeed it would be. But that would mean having 2 things to disconnect instead of one. More margin for error. Of course, any diligent spark would...
Replies
6
Views
680
loz2754
L
  • Question
Why would the RCD fail … yes it can happen but then it may not. Without it you have no protection on the TT System
Replies
36
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top