Afternoon all been a while since I've posted.


at today's job I noticed 10mm meter tails with 6mm bonding and although my first thoughts were tails should be min 16mm and bonding 10mm

so at the risk of sounding stupid I couldn't find the exact reason why this was wrong as the 10mm would take 61amps

could anyone clear this for me?
 
V/Ze= 766A

I=766
T=0.16
K=143 (not incorporated in a cable or bunched)

766x766=586756

586756x0.16=93880

square root of 93880=306

306/143=2.13mm for your main earthing conductor.

Taking reg 544.1.1 in to account the 6mm bonding conductor is adequate.

Edit: Based on a BS1361 fuse

Hi Lee or anybody else. Can you confirm what the T value of 0.16 relates to with this calculation?

Thanks
 
V/Ze= 766A

I=766
T=0.16
K=143 (not incorporated in a cable or bunched)

766x766=586756

586756x0.16=93880

square root of 93880=306

306/143=2.13mm for your main earthing conductor.

Taking reg 544.1.1 in to account the 6mm bonding conductor is adequate.

Edit: Based on a BS1361 fuse
Hi Lee or anybody else. Can you confirm what the T with value of 0.16 relates to here?

Thanks
 
The supply authority and utility provider will expect to see 16mm tails and therefore a 10.0mm bond is required to satisfy their requirements also. The regs and calculations can determine other values but to ensure you meet the minimum requirements of the energy supplier this is what I would install as a contractor.
 

Reply to 10mm meter tails 60amp fuse 6mm bond in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
388
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
970
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top