10mm T&E for Consumer unit supply | Page 3 | on ElectriciansForums

Discuss 10mm T&E for Consumer unit supply in the UK Electrical Forum area at ElectriciansForums.net

S

Sav

Morning everyone,

Hope your all well.

Just a a quick question. We have been asked to quote for a HMO conversion, in a domestic property. So basically, the developer buys these houses and makes rooms out if them.
Leach room is basic, small ensuite shower ( not electric ), lights and a few sockets. There is a communal kitchen and each room is supplied by its own consumer unit.
There are 2 circuits, lights and sockets.
What I'm asking is, the consumer units are fed via 10mm T&E that go down to 60A isolators, which in turn go into a big Henley block.
There are about 5 rooms, so five isolators.
I would have thought that the consumer units for each room , from the isolators had have 16mm earth ?
Obviously things like communal smokes and fire alarm system etc are fed from landlord board.
The supply is a TN-S single phase

regards,
sav
 
Can I just ask, why are some guys speccing SWA when it is within the confines of a domestic dwelling??? Are we anticipating the occupants to be trying to dig the place up?
 
Re: 10mm T&E for Consumer unit supply

Oops:lipsrsealed2:

Hey thats why Im banned from texting especially when trying to get into some women's ........

So just out of interest, and I am by no means fluent in this aspect, but, Im led to believe that discrimination or even partial discrimination is not possible between MCB and MCB.

It depends entirely on the prospective fault current. Discrimination for the purpose of overload protection is entirely affordable though.

- - - Updated - - -

Can I just ask, why are some guys speccing SWA when it is within the confines of a domestic dwelling??? Are we anticipating the occupants to be trying to dig the place up?

Because that's what the OP said the customer asked for.

Are you happy to bury a non-RCD protected T+E submain in the wall then?
 
Re: 10mm T&E for Consumer unit supply

It depends entirely on the prospective fault current. Discrimination for the purpose of overload protection is entirely affordable though.

- - - Updated - - -



Because that's what the OP said the customer asked for.

Are you happy to bury a non-RCD protected T+E submain in the wall then?
No of course not, there would be an RCD protecting each one, as someone has already suggested. No one is going to price for SWA and expect to get the job???
 
Yes overload I understand, but with short circuit its more complicated. I thought cascading/discrimination was usually in the ratio 2:1 with fuses or perhaps a mixture of fuses and MCBs. Although I've read that you need the downstream device to have a total I2t less than the pre arcing I2t of the upstream device, I've yet to get round to fully grasping this aspect and to be honest have never been in a situation where I've need the knowledge. Perhaps I need to read up on this and maybe start a new thread.:smile5:
 
Re: 10mm T&E for Consumer unit supply

No of course not, there would be an RCD protecting each one, as someone has already suggested. No one is going to price for SWA and expect to get the job???

An RCD up front and then another in the board?!

Dunno where you get your SWA from but I get it cheaper that T+E.
 
Loads of switch fuses and henly block dont like the sound of that,, one main switch to isolate the Complete supply then one decent TP CU with single phase conversion kit , with a circuit supplying each Flat, if its a new install the i would use a 3 core swa and use 16mm reason for this is if they decide to up grade the flats in the future then the supplies are there , always plan for the future
 
Yes overload I understand, but with short circuit its more complicated. I thought cascading/discrimination was usually in the ratio 2:1 with fuses or perhaps a mixture of fuses and MCBs. Although I've read that you need the downstream device to have a total I2t less than the pre arcing I2t of the upstream device, I've yet to get round to fully grasping this aspect and to be honest have never been in a situation where I've need the knowledge. Perhaps I need to read up on this and maybe start a new thread.:smile5:

That only applies to fuses. What you don't want to have is a situation where a circuit tripping a downstream device causes the upstream fuse to have to 'prepare to trip' to use a phrase. Pre arcing is a state where the fuse is subjected to the fault current but has not yet tripped. The more this happens the more damaged the fuse becomes.

Say for example you have a DB where the highest rated MCB is 50A and you plan to supply this via a sub main. If for example you choose a 63A fuse and it has a prearcing current of 45A (it won't have, this is purely an example) then this is bad design. You would need to uprate the supply fuse or, if possible, downgrade the downstream device.

A very simplistic explanation I know.
 
Loads of switch fuses and henly block dont like the sound of that,, one main switch to isolate the Complete supply then one decent TP CU with single phase conversion kit , with a circuit supplying each Flat, if its a new install the i would use a 3 core swa and use 16mm reason for this is if they decide to up grade the flats in the future then the supplies are there , always plan for the future

And you've just priced yourself out of the work! :D
 
Re: 10mm T&E for Consumer unit supply

An RCD up front and then another in the board?! Ah yes good point, each room would have to have it's own RCD or it would take out the whole lot. Could you not use a 100mA time delay RCD in a CU after the meter, and then 30mA in each individual CU, that way protecting the T&E?

Dunno where you get your SWA from but I get it cheaper that T+E.
I must check my supplier then, that seems mad!!
 
Well, evidently thats far too expensive and you'll never in a month of sundays win the job, cos I'm priceing to have one shower unit RCD CU in the basement and just split off this 40amp MCB with 4mm flex for each flat clipped direct to the stairwell walls using metal clips with a 13amp FCU in each flat for 1 socket and, further fused down with an 3amp FCU for lights :wacko:
 
Re: 10mm T&E for Consumer unit supply

Could you not use a 100mA time delay RCD in a CU after the meter, and then 30mA in each individual CU, that way protecting the T&E?

Additional protection for a T+E cable buried less than 50mm in a wall can only be afforded by a 30mA RCD

I must check my supplier then, that seems mad!!

Not really, SWA is far cheaper to produce than T+E
 
Re: 10mm T&E for Consumer unit supply

Can you explain what you actually mean? So are you saying put a front end 30mA RCD on each supply to each flat with T&E submain burried?
No, I didn't make myself very clear I admit. I was initially suggesting only one RCD in a CU that would then feed each individual CU, but I now realise after giving it more than 10 secs thought that this would be crap. However, could you not use the method i suggested in my reply to D Skelton? I was not advocating having a buried T&E with no RCD protection!
 

Reply to 10mm T&E for Consumer unit supply in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

I've seen a few posts here which tend to suggest that wiring in a motorhome (or caravan) wouldn't be subject to normal inspection rules, but even...
Replies
0
Views
312
  • Question
What is the distance from the point outside the house to the shed?
Replies
8
Views
730

Recommended Sponsor News

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top