When caring out an EICR on a site I found that the 110 volt socket outlets were connected as three 2.5mm ring final circuits each protected by a 32 amp MCB (single Pole) in a DB fed from 110 volt transformer ,These sockets are used to supply halogen Flood lights that area plugged in when required ,there is about 10 on each circuits

Now I know this is not the correct way of doing it ,as I would of installed radial circuits protected via 16 amp double pole MCBs

There for due to the possible over load of the 16 amp sockets and the fact that there is no over current protection on the return leg I gave this observation a code 2

Am I being over the top as this installation has been in use for a least 10 years and is showing no signs of thermal effects

As thinking about it ,the lights that are being used will not overload the sockets and the 2.5mm ring can not be overloaded as the 32amp mcb would trip out ,

Only problem is any other appliance could be plugged into the 110 volts sockets so this was also my thinking for the code 2 observation
 
Think about it, you say you have 110v sockets connected to a 230v supply, what would be the implications of someone plugged a 110v appliance into the socket? BOOM comes to mind
 
Think about it, you say you have 110v sockets connected to a 230v supply, what would be the implications of someone plugged a 110v appliance into the socket? BOOM comes to mind
He never said the 110V sockets were on a 230V supply, they are fed from a 230V - 110V transformer via 32A MCB's. What he is saying is, anybody can come along and unplug the lights to plug in other pieces of equipment, which could draw more current than the lights.
 
He never said the 110V sockets were on a 230V supply, they are fed from a 230V - 110V transformer via 32A MCB's. What he is saying is, anybody can come along and unplug the lights to plug in other pieces of equipment, which could draw more current than the lights.

So he did must read the posts properly, my mistake
 
The same regs that define standard ring and radials at 230v also apply to 110v systems and quite rightly where you point out the lack of O/L protection due to the nature of 110v plugs not having integral fusing then you need to code accordingly as you would any other circuit with no sufficient O/L protection.

If the install is indeed 10yrs old then its more luck than judgment that has seen no issues, it was required back then and is required now to have O/L protection to ensure the outlets cannot be overloaded with loop-in lighting or multiway outlets.
 
The same regs that define standard ring and radials at 230v also apply to 110v systems and quite rightly where you point out the lack of O/L protection due to the nature of 110v plugs not having integral fusing then you need to code accordingly as you would any other circuit with no sufficient O/L protection.

If the install is indeed 10yrs old then its more luck than judgment that has seen no issues, it was required back then and is required now to have O/L protection to ensure the outlets cannot be overloaded with loop-in lighting or multiway outlets.
yes i agree i will recomend to change the db and fit 16 amp double pole mcbs tne current db is site made ,to be fair i dont know why a 240 volt circuit wasnt installed as these are just fixed halogen lamp that shine into the back of lorrys on loading bays .
 
yes i agree i will recomend to change the db and fit 16 amp double pole mcbs tne current db is site made ,to be fair i dont know why a 240 volt circuit wasnt installed as these are just fixed halogen lamp that shine into the back of lorrys on loading bays .

Some sites require 110v when leads are trailing across floors and won't allow 230v.
 
Yes but this set up just has an 110 volt socket at the loading bay door with a 110 volt halogen lamp fiited to the wall on a braket so ths light can swing into tne back of the trailer the flex from the light is the correct length to fit into the socket and so not trailing any ware , all oyhet sites i have been on have a 240volt set up
 
Yes but this set up just has an 110 volt socket at the loading bay door with a 110 volt halogen lamp fiited to the wall on a braket so ths light can swing into tne back of the trailer the flex from the light is the correct length to fit into the socket and so not trailing any ware , all oyhet sites i have been on have a 240volt set up
 
Yes sorry to clarify I have coded them separately as code 2 observations , all i was saying was that if they had been double pole 32 amp mcbs and the installation was to a good standard which it wasn't I would off been edging to a code 3 observations due to the use of the installation and no signs of thermal damage , its just the part were there is no OL protection for the individual lights but is this required ?

Can an 500 watt halogen light course an over load for example when the lamp blows and pull more than 16 amps and so possibly coursing damage to the 16 amp socket or to the 1.5mm flex supplying the light . I don't think it would and not sure of the maths if any to work this out
 

Reply to 110 volt 16 amp sockets on a 32 amp ring in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
959
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
This is an interesting issue. I agree with you however I took this to task with a scam inspector some years ago and we agreed to disagree that...
2
Replies
29
Views
2K
In Theory that’s a good argument but if you will be adding or moving switches or sockets or adding lights you’ll more than likely end up needing a...
Replies
7
Views
468

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top