when installing 12v lights how do you calulate the csa/cable length ?

i know that a 50w lamp would pull 4.16a @ 12volts so cable sizes have to be larger,
but how would you calcuate the maximum length of that cable? assuming your using twin and earth clipped direct ?

thanks in advance
 
so to work out the volt drop you 1st find out the mV/a/m for the cable, 2.5 = 15 (pg 275 brb) times this value by Ib which would be 50 watts (4.16 amps) then times by how many meters say 6 then divide by 1000

15 x 4.16 x 6 / 1000 = 0.3744
 
We tested an installation a while ago and the ELV lighting had been done through 250VA transformers, each feeding 5 downlights.

The runs varied between 1 and 10 metres and the fittings on the longer runs were so much dimmer than the rest!

The moral is to keep the 12V run to an absolute minimum, it's trouble!
 
also is a driver and a transformer the same thing??

IQ did you increase the csa to overcome the dimmer light?

We installed local transformers, not just for the dimming problem but the wiring was a shambles too.

A driver might be for LED lighting.
 

Reply to 12v cable lengh/csa in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
224
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
1K
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

  • Question
Well another week passed and I still don't have a proper answer to where the process is wrong. To reiterate, this is not a question for a real...
Replies
2
Views
276
Good question now to start with thermosetting insulated conductors are not tri-rated that is something different. Table 4E1A deals with this type...
Replies
1
Views
292

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top