Hi, I've been asked to install 13amp supply for a hot tub around 30m from the house.

Supply to property TN-C-S

Plan is to run a 4mm 2 core swa from a 16 amp mcb in the CU to a IP66 RCD switched fused spur (Aprox 25m from house)

Use the armour as the earth until it reaches the Rcd spur in which case I will heat shrink swa and then fit stuffing gland to terminate.

Earth rod with 10mm to the RCD spur and TT the rest.

Any advice would be great
 
is the TT earth just cos of the distance from the house? my mate got a jacuzzi hot tub installed a couple of years ago. they insisted on an electrician being on site when it was delivered. but i believe the standard install is just swa from the tub to an isolator switch nearby, and then fed back to the CU with RCD protection.
 
So if you need to TT will be based on whether if the PEN drops out is there a risk of a return path, from a fault through your body to true earth.

I have a hot tub and I have a PME but I have not TT'd it. The hot tub is all plastic and there is not extraneous conductive parts or exposed conductive parts anywhere near. The water heater is double insulated.

So if there is a fault there is no metallic parts for the live conductor to touch and bring the hot tub to live potential and the water heater is double insulated and it does not actually come into contact with water. It surrounds the plastic pipe that the water travels through.

So in my case installing an earth rod is a completely pointless exercise.
 
Hi, I've been asked to install 13amp supply for a hot tub around 30m from the house.

Supply to property TN-C-S

Plan is to run a 4mm 2 core swa from a 16 amp mcb in the CU to a IP66 RCD switched fused spur (Aprox 25m from house)

Use the armour as the earth until it reaches the Rcd spur in which case I will heat shrink swa and then fit stuffing gland to terminate.

Earth rod with 10mm to the RCD spur and TT the rest.

Any advice would be great
Thanks for the dumb all I asked was how you would get the 10mm into the spur/FCU an answer would have been sufficient if its advice you want from me then forget it.
 
That's what I asked the O.P.
thats ok ant ,your are only asking what I'm thinking ,nowt.
[ElectriciansForums.net] 13amp Hot tub supply
 
I do feel these 'like, dislike, agree etc etc' icons create more negative responses, than they set out to achieve.

I mean, why is there a 'bad spelling' icon. Do I need some ---- on here to tell me, when someone has posted a reply with incorrect spelling & grammar??

I could of said, 'I mean, wheir is their a 'bid spelling' icen. Do I nead some twot on hear to till me, when someone has pisted incurrect spilling & grammer'. :D
 
Tescos and BM seem to selling a lot of LayZspa hot tubs at the moment.
The Hot tub itself is inflatable, like a large paddling pool.
The pump/heater/bubble maker is a separate unit with quite a long lead which has a 10mA in line RCD.

The pump unit is waterproof, though I have not found an IP rating. The unit has to be next to the tub to connect the pipework and so the controls can be reached.
we have that one. it's exactly as you posted. the biggest drawback is the leccy bill.costs about ÂŁ20/week.
 
I do feel these 'like, dislike, agree etc etc' icons create more negative responses, than they set out to achieve.

I mean, why is there a 'bad spelling' icon. Do I need some **** on here to tell me, when someone has posted a reply with incorrect spelling & grammar??

I could of said, 'I mean, wheir is their a 'bid spelling' icen. Do I nead some twot on hear to till me, when someone has pisted incurrect spilling & grammer'. :D
If you are referring to Pete999 I think calling him a twot is a bit strong.:p;)
 

Reply to 13amp Hot tub supply in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
380
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
956
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Thanks for that guys I was more thinking about difference in potential between the tub and wet paving flags . The tub is plastic . But it’s the...
Replies
7
Views
1K
  • Question
Why would the RCD fail … yes it can happen but then it may not. Without it you have no protection on the TT System
Replies
36
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top