Hi, I've been asked to install 13amp supply for a hot tub around 30m from the house.

Supply to property TN-C-S

Plan is to run a 4mm 2 core swa from a 16 amp mcb in the CU to a IP66 RCD switched fused spur (Aprox 25m from house)

Use the armour as the earth until it reaches the Rcd spur in which case I will heat shrink swa and then fit stuffing gland to terminate.

Earth rod with 10mm to the RCD spur and TT the rest.

Any advice would be great
 
4mm - 13A???

Earth rod - why?

I would fit a socket if the customer is having a hot tub company deliver it as they will only want to see a socket.

I’ve had a few call outs where they have used a standard plug & socket, couldn’t remove the plug as it had melted onto the socket..

One of them shouldn’t have been on a 13a plug, as it was rated at about 3.2 kw.
The hire company had used a commando plug to 13a converter
 
Hi, I've been asked to install 13amp supply for a hot tub around 30m from the house.

Supply to property TN-C-S

Plan is to run a 4mm 2 core swa from a 16 amp mcb in the CU to a IP66 RCD switched fused spur (Aprox 25m from house)

Use the armour as the earth until it reaches the Rcd spur in which case I will heat shrink swa and then fit stuffing gland to terminate.

Earth rod with 10mm to the RCD spur and TT the rest.

Any advice would be great
Heat shrink the SWA? I take it you mean connect the armour to the Earth terminal in the FCU? Advice use a banjo on the SWA and use some suitably sized wire from there to the terminal, If I read your intentions correctly that is not the way to install this SWA, have you done any calculation for cable sizing. or is this a stab in the dark job. a stuffing gland is not the correct method, well you did ask.
 
For give me if I'm wrong on the earthing arangement.

I have around 80m of 4mm swa in my garage that needs using up should have stated that in original post.

I'm going to have to ring up the hot tub company as it only say on there website 13amp supply. Could really do with a power spec
 

Reply to 13amp Hot tub supply in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
771
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
978

Similar threads

  • Question
Thanks for that guys I was more thinking about difference in potential between the tub and wet paving flags . The tub is plastic . But it’s the...
Replies
7
Views
2K
  • Question
That was my saying not long ago about TNS to PME system. I would be nice you can ring up the DNO, will the systems being up graded, there is a...
Replies
9
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top