Yes but with the load after diversity being more than the existing incoming supply (100A TP) without even considering the existing load I kind of assumed that conversation would be happening anyway.
Ok i'll play the game here.
Assuming they are split as equally as possible (5,5,4) and as you used 230V in your earlier calculation i'll assume they are rated 9.5KW at 230V.
Total connected load on L1 = 5 * 9.5KW = 47.5kW = 197.9A
Allowable diversity if you consider thsi to be a boarding house = 100% FLC of largest 2 appliances + 25% FLC of all other appliances
Current for 1 * 9.5KW unit = 39.6A
Load after diversity = (2*39.6)+(3*(39.6/4)) = 79.2 + 29.7 = 108.9A
However you could consider these to be individual dwellings in a block then you take 100% FLC of the shower in each dwelling so we get back to 197.9A.
Either way that's going to be a bit much for your existing 100A supply
Yes you can dave OSGyou can not applly dievesirty to intantaious water heaters
So nobody is going to come up with a load per phase then !