Pme should not be used in agricultural buildings unless a metalic earth grid system with multiple access points for testing is installed.
What type of buildings are these, metal framed.? If im reading your posts correctly that the 1st submain goes into a cottage then alsong as that zs figure is ok and all bonding in place i see no problem with that, i would then be thinking the first farm building should be tt with upfront s type rcd, then each building daisy chained off the buildings one to the next with suitable ocpd. Bonding each building frame work as you go along, aslong as 10mm cpc loops from one building to the next. If cpc/swa are smaller or only 2c is usedyou may need to individual tt each building.
What type of buildings are these, metal framed.? If im reading your posts correctly that the 1st submain goes into a cottage then alsong as that zs figure is ok and all bonding in place i see no problem with that, i would then be thinking the first farm building should be tt with upfront s type rcd, then each building daisy chained off the buildings one to the next with suitable ocpd. Bonding each building frame work as you go along, aslong as 10mm cpc loops from one building to the next. If cpc/swa are smaller or only 2c is usedyou may need to individual tt each building.