Pme should not be used in agricultural buildings unless a metalic earth grid system with multiple access points for testing is installed.
What type of buildings are these, metal framed.? If im reading your posts correctly that the 1st submain goes into a cottage then alsong as that zs figure is ok and all bonding in place i see no problem with that, i would then be thinking the first farm building should be tt with upfront s type rcd, then each building daisy chained off the buildings one to the next with suitable ocpd. Bonding each building frame work as you go along, aslong as 10mm cpc loops from one building to the next. If cpc/swa are smaller or only 2c is usedyou may need to individual tt each building.
 
is the farmhouse off the same supply? I think that further to exact calcs you will exceed max Zs that's only one aspect what is the aprox average load at each building as for volt drop.From what you have posted this distance is not in a staight line but each building has been added in turn.A better set up would of been out to each building from D.B. at farmhouse what would the longest run of been then ?.

Not sure ive ever encountered a set up where multiple outbuildings have individual supplies, usually theseare add on after add on!
 
So the 50Mtr run is being added from the garage therefore what is the Zs at this point can the 63A B mcb disconnect in time.
 
Hmmm, quite bizarre. I was about to start a thread (hypothetical one!) on a similar tangent, but I'll let this one run in case the answer to my question comes up, and I save myself any unpleasant embarrassment. :)

As this thread seems to have stalled, I will ask my question, and it may be pertinent in any case.

I was reading through the December issue of Professional Electrician, and there's a piece by Elecsa 'The earthing functions that can be performed by the armouring of a cable'.

On reading through it, I noted a passage that said in a PME installation 'the armouring (or a core) should not be used as a main protective bonding conductor', may have to carry sustained high currents which may result in heating of the bonding conductor.

It's a lift from GN8 (page 54) 'For installations forming part of a TN-C-S system in which the supply is earthed at multiple points (PME conditions applying), and it is intended to utilise the armouring of a cable or a core of an
armoured cable as a protective bonding conductor the designer needs to consider the effects of the currents that may flow in the conductor due to network conditions. The armouring or a core of such a cable is normally not used as
a protective equipotential bonding conductor where PME conditions apply unless the electrical installation designer determines that the heat produced in the armouring or core due to its use will not cause overheating of the live conductors of the cable when on full load'.

So my question (could be embarrassing) is how does the designer make that determination?
 
... I noted a passage that said in a PME installation 'the armouring (or a core) should not be used as a main protective bonding conductor' ... as may have to carry sustained high currents which may result in heating of the bonding conductor ... unless the electrical installation designer determines that the heat produced in the armouring or core due to its use will not cause overheating of the live conductors of the cable when on full load'.
So my question (could be embarrassing) is how does the designer make that determination?

Never embarrassing, it's a good one MW !
Sounds like a hint not do it :)
Never one to be shy : if the sub main cable was selected as if the included bonding conductor was a live conductor then any long duration earth current should not overheat the cable (?). But I can't make the same statement about the armour as it hasn't been tested that way.

The next problem is the bonding conductor to the outbuildings could be required to be quite big with PME, bigger than the submain conductors (gulp). There's a good example of this in GN8 p70 Fig 5.15. Another reason to TT the outbuildings I guess.
 
You cannot rely on PME for socket outlets on Jetty and Pontoon fixtures and in Caravan Parks, so I suspect a similar regulation will apply in a farm installation as described??
 
As this thread seems to have stalled, I will ask my question, and it may be pertinent in any case.

I was reading through the December issue of Professional Electrician, and there's a piece by Elecsa 'The earthing functions that can be performed by the armouring of a cable'.

On reading through it, I noted a passage that said in a PME installation 'the armouring (or a core) should not be used as a main protective bonding conductor', may have to carry sustained high currents which may result in heating of the bonding conductor.

It's a lift from GN8 (page 54) 'For installations forming part of a TN-C-S system in which the supply is earthed at multiple points (PME conditions applying), and it is intended to utilise the armouring of a cable or a core of an
armoured cable as a protective bonding conductor the designer needs to consider the effects of the currents that may flow in the conductor due to network conditions. The armouring or a core of such a cable is normally not used as
a protective equipotential bonding conductor where PME conditions apply unless the electrical installation designer determines that the heat produced in the armouring or core due to its use will not cause overheating of the live conductors of the cable when on full load'.

So my question (could be embarrassing) is how does the designer make that determination?

For anyone interested, I posed my question to Elecsa technical and received this reply;

As you have already stated one needs to consider the possibility of the conductors overheating.
'Where PME conditions apply, the use of the armouring of the cable as a main bonding conductor may result in overheating of the live conductor where they are to be operated at significant proportion of their current-carrying capacity for sustained periods or at higher ambient temperatures.

Overheating of a live conductor in this context is where the conductor operating temperature exceeds the rated value appropriate to the insulation material such as 70® for thermoplastic (general purpose PVC)which can lead to premature ageing and deterioration of the insulation

Such over heading may be due to the diverted neutral currents or network circulating currents

The probability of the live conductor overheating due to diverted neutral currents is likely to be reduced if

(1) Where the cable is lightly loaded, bearing in mind that the heat produced in a conductor is proportional to the current squared and the ambient temperature is in the normal

(2) Where it is expected that the armouring will not carry a significant magnitude of diverted neutral current

Where the electrical installation designer considers that a reasonable probability exist of overheating being caused to the live conductor of the cable due to diverted neutral currents in the armouring, the armouring should not be used as a main bonding conductor.

Where after careful consideration the electrical installation designer decides that using the armouring of the cables as a main bonding conductor would not result in overheating of any of the live conductors, the armouring may be put to use provided its cross sectional area if sufficient to meet the requirements of regulation 544.1.1.'

Still none the wiser, but guess it's only going to be an issue in high load situations, unless someone can tell me differently?
PS I did ask about 'the armouring (or a core)'.

 
I'm interested :)

I think the SWA armour is pretty much never going to be suitable for bonding an outbuilding in a TNCS installation. Here's my reasons : we need the steel armour of the SWA to have the same resistance as the copper from Table 54.8 and that means x8(ish). And from Reg 544.1.1 if it's TNCS at the origin of the installation then it's the incoming DNO neutral size thats used in Table 54.8 and it sets the bonding size for any outbuildings using the origin TNCS. A good example is in GN8 figure 5.15.
 
The whole point of assessing the size of the armour is to ensure it is adequate to carry any diverted current. This is why it often is not practical because the csa of the cable is often larger than essentially required.
 
Elecsa response was about using the armouring not a core. GN8 says 'The armouring or a core of such a cable is normally not used as a protective equipotential bonding conductor where PME conditions'?
 
Elecsa response was about using the armouring not a core. GN8 says 'The armouring or a core of such a cable is normally not used as a protective equipotential bonding conductor where PME conditions'?
"Normally not" would not mean that you could not as long as it is correctly sized.
 

Reply to 150m submain to multiple outbuildings earthing (PME) in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar threads

I assume said contractor is part of a Part P scheme (NICEIC, Napit, few others..) in which case complain to them. They'll investigate (in theory)...
Replies
10
Views
793
I can't help wondering about earthing arrangements and how important aesthetics really are when attempting to make the best of a less than ideal...
2
Replies
21
Views
1K
nicebutdim
N

Recommended Sponsor News

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top