This is not really something I have ever had to deal with. Always done commercial submains which have been tns. But as an electrician are we allowed to just change the earthing system as it suits us? I thought that kind of thing was down to dno.
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss 150m submain to multiple outbuildings earthing (PME) in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
The same would apply with TN-S the armour must be suitably sized. To overcome the problem of armour inadequacies you can create a TT earthing system.This is not really something I have ever had to deal with. Always done commercial submains which have been tns. But as an electrician are we allowed to just change the earthing system as it suits us? I thought that kind of thing was down to dno.
"Normally not" would not mean that you could not as long as it is correctly sized.