Hi everyone,

Just a quick question I hope I can get some advise on.

Saw a 1 bedroom purpose built 1st floor flat last night that is in need of a rewire.

The consumer unit is the old rewire-able type with 16mm T&E on supply side.
Although its red and black on the 16mm, it does look newish (10 years may be), but obvious tests will need to be carried out.

In the basement, which the customer does not have access too ( my FP2 key does not fit either, as it has some kind of security lock), I would have presumed there must be an isolator to this flat, as well as the other 5 flats on this block.
Again, this would need examining when the time comes.

I mentioned to the builder who is going to be carrying out building works, that we must check and upgrade the earthing accordingly, and also bring a 16mm earth to the consumer unit.
His guy, who also does electrics, said that the 16mm T&E along with its 6mm earth is more than adequate.

I have always bought in 16mm earth to the consumer unit, as thats what we were told to do on sites etc.

Am I missing something???

Thanks and regards,
Sav
 
At the moment we do not know the earthing arrangement of the premises.

If its PME then table 54.8 comes into play re the bonding and if TNS or TT the csa should be not less than half the csa of the required earthing conductor with a min of 6mm!
 
According to GN8, the main bonding is sized to the DNO's incoming Neutral supply cable, not the downstream local neutral supply cable to the individual flat, it should not be less than 35mm in the case of PME supplies.
It is a little odd in the the main bonding conductors can have a greater csa than the local Live supply (to each flat CU) conductors.

In all other cases (TT, TNS) the main bonding is sized to be not less than half of the Earthing conductor.

At least that is how I read it (GN8).
 
Last edited:
At the moment we do not know the earthing arrangement of the premises.

If its PME then table 54.8 comes into play re the bonding and if TNS or TT the csa should be not less than half the csa of the required earthing conductor with a min of 6mm!

Agreed , but table 54.8 applies to the main protective bonding ,which is in the basement , where the gas and water services enter the building.
Not relevent to where the services enter each flat.
Unless your suggesting that there needs to be 2 sets of main protective bonding conductors , basement and flat ?


I do like a healthy technical debate lol.
 
To Add,

If each flat is PME, the earthing conductor to each flat has to be a minimum of 35mm, (again sized to the DNO's incoming Neutral), as it has to satisfy as a combined CPC and main bonding conductor (Pg 52 GN8).
 
This is getting to be like pulling teeth...lol!!

Every flat, (be there 2 or 20 flats) will each require a main protective bonding installation, REGARDLESS of the main protective bonding arrangements made at the buildings service head and main distribution centre and where the main services enter the building (eg, gas & water).
 
Last edited by a moderator:
Agreed , but table 54.8 applies to the main protective bonding ,which is in the basement , where the gas and water services enter the building.
Not relevent to where the services enter each flat.
Unless your suggesting that there needs to be 2 sets of main protective bonding conductors , basement and flat ?


I do like a healthy technical debate lol.

Main protective bonding conductors are required in every flat in Multi Occupancy Premises regardless to what is connected outside that premises!
 
To Add,

If each flat is PME, the earthing conductor to each flat has to be a minimum of 35mm, (again sized to the DNO's incoming Neutral), as it has to satisfy as a combined CPC and main bonding conductor (Pg 52 GN8).

But the flats aren't pme , tt , tns or anything else , they're supplied via a privately
owned sub-mains ? so not entirely relevent.
 

Reply to the thread, titled "16mm Earth main protective conductor" which is posted in UK Electrical Forum on Electricians Forums.

Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Daily, weekly or monthly email

Back
Top