Did a job earlier in a new build, part of a 5 year old new build estate in the darkest depths of kent. Anyhow opened up CU and saw 16mm tails so assumed would be on 80a fuse as there not huge demand. Then outside to check service head and main fuse is labelled 100a ?, the tails are 16mm t&e.
I did nor remove the fuse carrier to check the actual fuse as it was sealed :rolleyes:

Anyhow my point is, ive already installed new circuit and have to issue an EIC, I will be writing in comments box write what I found and that it looks wrong. However looking forward what should I do about this. The customer wont be happy me turning off all the power; I told him to contact the people he bought the house from and raise the point.

Another thing I found includes a spur that don't switch off the load in garage that its labelled to do. Its not right is it, brand new house as well, and theres hundreds of them.
 
Did a job earlier in a new build, part of a 5 year old new build estate in the darkest depths of kent. Anyhow opened up CU and saw 16mm tails so assumed would be on 80a fuse as there not huge demand. Then outside to check service head and main fuse is labelled 100a ?, the tails are 16mm t&e.
I did nor remove the fuse carrier to check the actual fuse as it was sealed :rolleyes:

Anyhow my point is, ive already installed new circuit and have to issue an EIC, I will be writing in comments box write what I found and that it looks wrong. However looking forward what should I do about this. The customer wont be happy me turning off all the power; I told him to contact the people he bought the house from and raise the point.

Another thing I found includes a spur that don't switch off the load in garage that its labelled to do. Its not right is it, brand new house as well, and theres hundreds of them.

The distributers protection (service head bullit) on a condition report should normally be recorded as a "LIM"...

Next, use your intuition to determine what the max. Demand for each supply is/should likely be...
P.S.
It won't be 80 chuffin amps...thats for sure...


The bigger issue here for me...is whether or not it complies with the requirements of certain DNO's in regards to length of run from the service head (usually 3 meters...i think)...
 
Last edited by a moderator:
Its not a sub main, its a semi detached house with its own single phase supply.

Submain Is the common name for any distribution circuit which is part of the consumers installation. The type of property or incoming supply is irrelevant, if it is a circuit with ocpd etc on the consumers side of the meter and it feeds a DB, CU etc then it is a submain.
 
Checked again today and switch fuse has an 80A. Took some pics of the t&e serving the CU, as you can see theres no glands, no cleats, no rcd to be found. Not sure if theres mechanical protection where the t&e goes into building; what are your thoughts on this. The building was constucted in 2016.
[ElectriciansForums.net] 16mm T&E tails on 100amp fuse
[ElectriciansForums.net] 16mm T&E tails on 100amp fuse
[ElectriciansForums.net] 16mm T&E tails on 100amp fuse
[ElectriciansForums.net] 16mm T&E tails on 100amp fuse
 
Last edited:
Glanding into the switch-fuse could be better. Looking at the photo's I am guessing that the 16mm T&E goes up into the cavity which can have its own non-compliant issues and then in joist space to consumer unit at ceiling height that way removing the requirement for RCD protection. Although in practice the house would not normally take 80A more like 40A and the 16mm can take that the cable should be rated more than the fuse rating. 80A is on the borderline of clipped direct.
 
Checked again today and switch fuse has an 80A. Took some pics of the t&e serving the CU, as you can see theres no glands, no cleats, no rcd to be found. Not sure if theres mechanical protection where the t&e goes into building; what are your thoughts on this. The building was constucted in 2016.
View attachment 48408 View attachment 48409 View attachment 48410 View attachment 48411

I might of glanded em if it were me...
But I've seen plenty of entry's into enclosures done like that...
The bit where they've appeared to have just brayed a hole in the side of whatever it is looks a bit dog Shyte though...
 
Checked again today and switch fuse has an 80A. Took some pics of the t&e serving the CU, as you can see theres no glands, no cleats, no rcd to be found. Not sure if theres mechanical protection where the t&e goes into building; what are your thoughts on this. The building was constucted in 2016.
View attachment 48408 View attachment 48409 View attachment 48410 View attachment 48411

I might of glanded em if it were me...
But I've seen plenty of entry's into enclosures done like that...
The bit where they've appeared to have just brayed a hole in the side of whatever it is looks a bit dog Shyte though...
 
A few years ago I took an Nic inspector to an EICR as part of my annual visit. It had 16mm tails but the cutout was an older type with 60a fuse. I had put the tail size was Ok for the fuse although I hadn't checked it physically (it was a 60a cutout). He argued the ---- with me. I said I hadn't removed it as it was sealed but it was a 60a cutout. He wouldn't leave it and made me confirm in writing after a physical inspection by DNO the size of the fuse!
 
Have the rules changed ?? Assess the maximum demand of the installation, if this does not exceed 60 Amps then 16mm tails are acceptable. I think NICEIC inspector told me this. Make a note on the certificate. It's important that any additions to the connected load do not exceed the rating of the tails.
Hibreasoning was that because I hadn't physically inspected the fuse it could be 100a protecting tails rated at say 80a.
 

Reply to 16mm T&E tails on 100amp fuse in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
Normally you'd install either a fuse-switch or a switchfuse at the incoming supply position rather than a DB, this gives you some hope of...
Replies
10
Views
1K
davesparks
D
In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...
Replies
11
Views
1K
  • Question
BS3871 type 3's have a similar shaped operating curve to BS60898 type C's. Any fault that will meet the disconnection time of 5s (for 63A...
Replies
5
Views
2K
  • Question
I wouldn't be happy with a 10.0 on a 60A fuse (I assume a 1361) especially not knowing the installation method.
Replies
4
Views
1K
  • Question
My bafflement increases. I swapped the offending light with one elsewhere on the back of the house - one of those that's on a circuit of its own...
Replies
5
Views
873

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks