A lot of flats use a 16mm pvcpvc te supply as long as its backed up with a 10mm CPC it should be fine. Don't forget it's protection at the meter if over a distance.
 
25mm tails and 10mm bonding is stated for new builds and rewires.

16mm tails and 6mm bonding is often acceptable, given certain situations and checks.

That sounds ridiculous to me for a one bedroom flat!! The DNO cut out fuse isn't going to be over 60A.
What is this obsession with 25mm tails these day's, i bet that in the vast majority of cases that installation is never going to see anywhere near 100A, and likely not see 80A either!!!
 
That sounds ridiculous to me for a one bedroom flat!! The DNO cut out fuse isn't going to be over 60A.
What is this obsession with 25mm tails these day's, i bet that in the vast majority of cases that installation is never going to see anywhere near 100A, and likely not see 80A either!!!

I think it's coming from the drawings in the on site guide lol!!!!
Not to keen on the book myself
 
I think it's coming from the drawings in the on site guide lol!!!!
Not to keen on the book myself

That's it exactly, I keep seeing 'BS7671 states 25mm tails' it doesn't, it states that cables must comply with the over current protective device!

I wonder how many have just the OSG rather than BS7671?
 
That sounds ridiculous to me for a one bedroom flat!! The DNO cut out fuse isn't going to be over 60A.
What is this obsession with 25mm tails these day's, i bet that in the vast majority of cases that installation is never going to see anywhere near 100A, and likely not see 80A either!!!

I completely agree.

But so many muppets think they have to upgrade the tails to 25mm when doing CU changes, which is mad given the amount of 60A fuses around.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
16mm tails
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
24

Thread Tags

Advert

Thread statistics

Created
ambrad,
Last reply from
SparkyDips,
Replies
24
Views
9,381

Advert

TrueNAS JBOD Storage Server

Back
Top