Been to a job today, rewire Immersion cct to suit new cylinder pos.
Did Zs got 12 ohm....looked a little closer...
Immersion fed from b16 breaker from main switch sub board.
Sub board fed via 16mm T&E submain from MCB on non RCD side of DB1. DB1 supplied direct from cutout, typical 16th split board, main switch 1 half 30mA the other. Earthing system TT.
Essentially half of this install, including cct I worked on, has no fault protection! Other than this, everything else looks properly done, am I missing something? My proposal is to replace the main switch with a 100mA RCD type, but question is S type or not? The RCD would protect final ccts as well as the distribution cct to sub board, and there is no 30mA RCD on sub board. So S type would not comply on disconnect times for finals, but a standard 100mA wouldn't necesarily provide selectivity! Looking for a simple but compliant solution please!
 
Hi - most likely the “cables in walls” reg will mean a 30mA rcd (non delayed) is now required for the circuit you’ve modified. I’d discuss with the Customer and try to fix the rest of them while you’re at it. Another thought is many old TT places now have PME available from DNO too.
 
Yep I could 30mA the final cct for immersion. But Zsdb at sub board is 12 Ohms....so an earth fault on T&E sub main would not trip any protective devices.
This, and the fact all the other non RCBO/non RCD side circuits are left unprotected bothers me.
On this occassion we haven't added any buried runs of T&E, all cabling is surface in plant room, so don't believe I'm required to install additional protection, but do think the installation should be protected against earth fault. Will ask UKPN about PME as might be simplest, but everywhere in this village seems to be TT, so may not be available.
 

Reply to 16th ed. Tt install...only 1 RCD in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
959
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Regarding the EV, it’s an Ohme charger which I believe has a type A RCD built in, setup would be: 50A RCBO to feed garage db Garage db has no...
2
Replies
17
Views
808
  • Question
Many thanks all. Very helpful to be able to bounce these things around. Was fairly happy with it all initially, but once the seed of doubt is...
Replies
8
Views
842

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top