Was talking about this with a couple of guys on site earlier and differing opinions were had. It seems the line quoted below has introduced some confusion.
"Metallic pipes entering the building having an insulating section at their point of entry need not be connected to the protective equipotential bonding (Regulation 411.3.1.2)."
Example 1. Some were of the thinking that for example an incoming iron water pipe that somewhere just above floor level had say a metre of plastic pipework before continuing in copper would never need bonding as it has an insulating section. Some were of the thinking you should test the pipework above and/or below the insulating section to see if it is extraneous.
Example 2. Some were of the thinking that any utility supply service that enters the building in plastic will never need bonding and some thought the internal pipework should be tested to see if it is extraneous.
What say you forum? I have my own thoughts I shall keep to myself for now...
"Metallic pipes entering the building having an insulating section at their point of entry need not be connected to the protective equipotential bonding (Regulation 411.3.1.2)."
Example 1. Some were of the thinking that for example an incoming iron water pipe that somewhere just above floor level had say a metre of plastic pipework before continuing in copper would never need bonding as it has an insulating section. Some were of the thinking you should test the pipework above and/or below the insulating section to see if it is extraneous.
Example 2. Some were of the thinking that any utility supply service that enters the building in plastic will never need bonding and some thought the internal pipework should be tested to see if it is extraneous.
What say you forum? I have my own thoughts I shall keep to myself for now...