Hello all.
Quick question: Are 17th reg 3rd amendment metal consumer units compliant with 18th edition regs?
eg Hager VML716RKO
Many thanks (Newbie)
If you look at the thread SC referred to above ^^^^ and read that reg (536.4.202) properly it is the design current for that RCD that needs to comply not the size of the company fuse etc, etc, , the last paragraph of that reg states manufacturers instructions should be followed, however in the same regs book, or at least in the 17th amd 3 book only states that manufacturers instructions should be taken account of.
Unlikely to hit 9mA in a domestic environment, besides which if you hit 10mA on a given circuit you are then into HI earthing, we hit this on office installs quite frequently where a lot of computers are installed.
Edit: 30mA RCDs tend not to trip until circa 22mA mark, @ 15mA they should not trip either.
Read Reg 536.4.202 again, and you will see it is the design current Ib that needs to be complied with, which is what most of us have always done anyway.
As said manufacturers instructions should be taken account of, not followed blindly.
Ps. Spin London was correct too it is also the ICn that is also important,
Seems like the manufacturers trying to pull a fast one to me.
Hit, nail and head...........
If anybody thinks that they need to make sure that each RCD value is equal to or less than the main fuse they are being mislead.
Take this another step and you shouldn't have the sum of the MCB's or RCBO's exceeding the DNO fuse ............. which is madness.
TBH I'm not sure what the average leakage per RCD is for a typical split load domestic board as I don't do a lot of domestic. I would still recommend full RCBO though for a number of reasons.
Derby
18th Edition Compliant Consumer Unit
RutlandFox,
Midwest,
TrueNAS JBOD Storage Server