18th Edition Compliant Consumer Unit | on ElectriciansForums

Discuss 18th Edition Compliant Consumer Unit in the UK Electrical Forum area at ElectriciansForums.net

Joined
Feb 24, 2019
Messages
28
Reaction score
6
Location
Derby
Hello all.

Quick question: Are 17th reg 3rd amendment metal consumer units compliant with 18th edition regs?

eg Hager VML716RKO

Many thanks (Newbie)
 
If you look at the thread SC referred to above ^^^^ and read that reg (536.4.202) properly it is the design current for that RCD that needs to comply not the size of the company fuse etc, etc, , the last paragraph of that reg states manufacturers instructions should be followed, however in the same regs book, or at least in the 17th amd 3 book only states that manufacturers instructions should be taken account of.
 
Probably best to supply full RCBO boards (with SPD) unless you can guarantee that your RCDs will be subjected to less than 9mA of earth leakage.
 
Unlikely to hit 9mA in a domestic environment, besides which if you hit 10mA on a given circuit you are then into HI earthing, we hit this on office installs quite frequently where a lot of computers are installed.

Edit: 30mA RCDs tend not to trip until circa 22mA mark, @ 15mA they should not trip either.
 
Read Reg 536.4.202 again, and you will see it is the design current Ib that needs to be complied with, which is what most of us have always done anyway.
As said manufacturers instructions should be taken account of, not followed blindly.

Ps. Spin London was correct too it is also the ICn that is also important,
 
Last edited:
Unlikely to hit 9mA in a domestic environment, besides which if you hit 10mA on a given circuit you are then into HI earthing, we hit this on office installs quite frequently where a lot of computers are installed.

Edit: 30mA RCDs tend not to trip until circa 22mA mark, @ 15mA they should not trip either.

[ElectriciansForums.net] 18th Edition Compliant Consumer Unit


TBH I'm not sure what the average leakage per RCD is for a typical split load domestic board as I don't do a lot of domestic. I would still recommend full RCBO though for a number of reasons.
 

Reply to 18th Edition Compliant Consumer Unit in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
959
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Ah my mistake - apologies. I have something more or less like this wylex unit and the flappy plastic cover has got a broken pin so won't stay one...
Replies
4
Views
275
  • Question
Personally, I would take a Ze measurement myself rather than rely on someone else's maybe drive by scrap of paper.
2 3
Replies
31
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top