They don't Captain Mainwaring.So if Mrs Miggins wants an additional light she will need an RCD, she won't like it, you know!
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss 18th edition final changes released by IET in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
They don't Captain Mainwaring.So if Mrs Miggins wants an additional light she will need an RCD, she won't like it, you know!
January 2019 is when we all need to comply, there’s still a window
I have a meeting with my scheme provider in a couple of weeks to tell us the in outs of it all, but I'm really interested to hear other people's take on it all beforehand.
And are they saying a copper gas pipe which has a plastic covering , but then connects to a copper pipe internal in the house no longer requires bonding?
Will it be deemed unacceptable to clip a cable on a joist , above a bedroom ceiling using twin and earth clips?
Generally cables installed above a plaster board ceiling with a minimum 30 minutes fire protection will not require metallic fixings.Sorry to repeat myself here , but I'm just interested in other people's take on a couple of things in the report.
Will it be deemed unacceptable to clip a cable on a joist , above a bedroom ceiling using twin and earth clips?
And are they saying a copper gas pipe which has a plastic covering , but then connects to a copper pipe internal in the house no longer requires bonding?
Maybe ( probably !!) I'm being thick and not grasping what they are saying .
I have a meeting with my scheme provider in a couple of weeks to tell us the in outs of it all, but I'm really interested to hear other people's take on it all beforehand.
Many peoples interpretation differ from many other, as I'm sure you are all aware .
It's almost as if if meant to confuse ( the whole regs book)
Why it isn't written in plain everyday English has always been of great annoyance to me.
We are sparks, not lawyers.
So do you think it means if the pipework being plastic rising from the ground and say connecting to an external gas meter , but then enters the property in copper pipe still requires bonding?Metallic pipes entering the building having an insulating section at their point of entry need not be connected to the protective equipotential bonding (Regulation 411.3.1.2).
I see this not as a plastic covering but as were the pipe has a metal section replaced with plastic (or other insulating material). Like where the water pipe coming into your house is replaced with plastic piping and later on it converts back to copper.
"A new Regulation 421.1.7 has been introduced recommending the installation of arc fault detection devices (AFDDs) to mitigate the risk of fire in AC final circuits of a fixed installation due to the effects of arc fault currents."
I would say that this would depend on the wording of the regulation.When you meet them please can you ask them my question in post #18... I'd be interested to hear what they say.
I agree with Ian1981 a plasterboard ceiling provides support in the case of a fire. It would only be high level cables surface clipped / plastic conduit / trunking within a room that would need the additional support.So, do people read that as , cables clipped on a joist , above a bedroom ceiling are no longer permitted to be held up with t&e clips?
The sheathed metallic pipe is a strange one as well.
Surely it still brings in a potential to the building? I'm not convinced all these engineers totally understand the science of it all. You just need to read the difference of opinions on the matter of earthing and bonding on here to realise there are many different takes on the matter.
I would say that the AQ conditions at their worst case for the UK always came out as SPD not needed therefore you would apply the later RA conditions of risks to life, property, etc. if you were considering it, so no real change.am I reading that right that SPD's might be more likely needed too?
Generally cables installed above a plaster board ceiling with a minimum 30 minutes fire protection will not require metallic fixings.
If it where the case we would need to be doing now on our works such as new builds where cables are installed above a ceiling to landing areas and halls just above your front doorway.
Metallic pipes entering the building having an insulating section at their point of entry need not be connected to the protective equipotential bonding (Regulation 411.3.1.2).
Has anyone actually seen such an install?
PS not having a dig at you Spoon!
Reply to 18th edition final changes released by IET in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net