Yes, the conduit would need to be secured with steel saddles to the side of the joistWould that apply to singles in PVC conduit laid between joists?
The fire rating of plasterboard was raised during the discussion, but this was not considered to meet the requirement for supporting wiring systems
Of course the plasterboard gives fire protection, upto 30 mins.Are you suggesting you will ignore this regulation?
521.10.202
Wiring systems shall be supported such that they will not be liable to premature collapse in the event of a fire.
This is a blanket requirement, no distinction is given to areas of wiring or type of installation. I have been informed that a plasterboard ceiling is not considered to provide support for cables in the event of a fire, and that all wiring throughout its length will require support with (for example) steel straps, unless it is drawn through joist holes.
This will have implications for rewires where cables are often fished through areas where floors are difficult or impractical to lift for access.
Hence my comment that the cables housed in the trunking will need metallic support against collapsePlastic trunking is not the issue here as it will melt in the fire. The idea is to stop entanglement of firefighters with the copper cables within the trunking.
How much vital information do you want? The regulation is very clear as far as I can see. Wiring systems must be installed to stay put and not collapse in the event of a fire. That clearly means they must be supported by fire resistant fixings to the structure of the building
Of course the plasterboard gives fire protection, upto 30 mins.
If it didn’t then we would have to regard the regulation regarding escape routes to domestic new builds currently to the 17th edition and provide metallic support above the plaster board ceiling in hallways to the exits which is completely unnecessary.
Never been pulled of an Niceic assessment on this.
Based on the information I have been given I think you are wrong, all of the guys on the course, including me took the same line s you regarding plasterboard, but the tutor insisted all wiring systems require support even if above a plasterboard ceiling. Plasterboard collapses during a fire, it may be the case that plastic water pipes will melt which will flood ceilings and cause collapse during a fire. The wiring above if not supported will collapse as well and not meet the requirements.Of course the plasterboard gives fire protection, upto 30 mins.
If it didn’t then we would have to regard the regulation regarding escape routes to domestic new builds currently to the 17th edition and provide metallic support above the plaster board ceiling in hallways to the exits which is completely unnecessary
Based on the information I have been given I think you are wrong, all of the guys on the course, including me took the same line regarding plasterboard, but the tutor insisted all wiring systems require support even if above a plasterboard ceiling. Plasterboard collapses during a fire, it may be the case that plastic water pipes will melt which will flood ceilings and cause collapse during a fire. The wiring above if not supported will collapse as well and not meet the requirements.
Funny but I think your tutor is wrongBased on the information I have been given I think you are wrong, all of the guys on the course, including me took the same line regarding plasterboard, but the tutor insisted all wiring systems require support even if above a plasterboard ceiling. Plasterboard collapses during a fire, it may be the case that plastic water pipes will melt which will flood ceilings and cause collapse during a fire. The wiring above if not supported will collapse as well and not meet the requirements.
How on earth would you fix cables running parallel between joists above a ceiling on a rewire or addition without major upheaval ?
All the above points were made on the course, I'm not arguing a case because I agree or don't agree, I'm simply telling you what I was told. And TBH I think the tutor is stating exactly what the guidance on this is likely to be. The IET do not take into consideration practicalities.
All the above points were made on the course, I'm not arguing a case because I agree or don't agree, I'm simply telling you what I was told. And TBH I think the tutor is stating exactly what the guidance on this is likely to be. The IET do not take into consideration practicalities.
Funnily enough this is almost word for word the objections raised on the course, however if you stop to think about what you have said you are suggesting the firefighters will give up and let the occupants die when ceilings collapse, they wont, and they don't need dangling wiring getting in their wayFunny but I think your tutor is wrong
By the time a plasterboard ceiling collapses then the house is pretty much done for
He must know more than most about the fire protection quality of plasterboard