Had these on the 18 th exam,confused me a bit.
What’s the maximum Rcd that can be used ,when an Earth electrode Reading is 2 ohms.
100 ma
300 ma
30 ma.
What would you say is the answer.
 
at my age, i won't be taking the 18th, but if it was anything like 17th, i'd finished in 50 minutes, scored 87%, and that was at the age of 65. i could have done a bit better if i'd taken the time to look a couple of things up, but the pub was open.
 
at my age, i won't be taking the 18th, but if it was anything like 17th, i'd finished in 50 minutes, scored 87%, and that was at the age of 65. i could have done a bit better if i'd taken the time to look a couple of things up, but the pub was open.
Yea this will be the last I do,done 14,15,16,17 th,this was the most difficultist,its the new regs that disturb you.
 
Not really sure what that question is about?
The maximum with an Ra of 2 ohms would be 25A, so all 3 of the answers shown, can be used.
Not aware of there being a limit of 100mA for TT installations.
Though I seem to recal something about 100mA max for fault protection and 300mA for fire protection?
However the question doesn’t mention fault or fire protection.
 
You can get earth leakage shunt relays which sense leakage by way of core balanced current transformers. These can be set for milliamps or amps but are not your run of the mill devices.
 
Had these on the 18 th exam,confused me a bit.
What’s the maximum Rcd that can be used ,when an Earth electrode Reading is 2 ohms.
100 ma
300 ma
30 ma.
What would you say is the answer.

Given the options I would say 300mA as that is the closest option to 20A.

However there are four options and you have only given us three.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

cliffed

Arms
-
Joined
Location
Worcester
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
18th edition question
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
26
Unsolved
--

Advert

Thread statistics

Created
cliffed,
Last reply from
Ffoeguk,
Replies
26
Views
3,059

Advert

Back
Top