Changing to built in double fan oven. 45A cooker switch which is supplied with 6mm from 20A mcb . Double fan oven is rated at 4.1kw.

4100/230=17.82

Would the flex be ok as it can carry up to 25A and less than a metre be used.

What do you guys suggest?
 
Why do people go on about ''Must be heatproof 90c rated''?? , are both the terminated connections rated 90c, i doubt it, certainly not at the wall accessory anyway, So the 90c cable then has to be derated to 70c anyway...


In all the years i've been around, i've never seen radiated heat damage from connected Cookers/Ovens that have been wired with Normal building wire, typically 6mm T&E. So i can't see any problem using a suitably current rated 70c rated flexible cable.
 
I don't rate flex myself, just trying to get the op to let us know what he thinks about it all, ever tried connecting a 2.5mm2 flex into a cooker terminal? if they come pre flexed great, but if not LOL, good luck sleeping at night, unless you know what your doing which is debateable here, wondered if the op had ever used it hence the questions, and if your going to use flex use HR for a cooker IMO, lets hope the cooker has a terminal block and not the type which most cookers have as connecting flex in one of those won't be an assured connection, for an enthusiast.
 
I don't rate flex myself, just trying to get the op to let us know what he thinks about it all, ever tried connecting a 2.5mm2 flex into a cooker terminal? if they come pre flexed great, but if not LOL, good luck sleeping at night, unless you know what your doing which is debateable here, wondered if the op had ever used it hence the questions, and if your going to use flex use HR for a cooker IMO, lets hope the cooker has a terminal block and not the type which most cookers have as connecting flex in one of those won't be an assured connection, for an enthusiast.


One would hope the appropriate crimped termination would be used at the oven's connection/terminal block... As you state unless the oven/cooker came with a factory fitted flexible cable, i'd stick with the old tried and proven method, of using appropriately sized T&E...lol!!
 
One would hope the appropriate crimped termination would be used at the oven's connection/terminal block... As you state unless the oven/cooker came with a factory fitted flexible cable, i'd stick with the old tried and proven method, of using appropriately sized T&E...lol!!
this is it....there seems to be this allergy to T&E for cookers..lol..
if they bothered to look they would realise that the cable comes into the cooker from the bottom...
so i suppose that heat don`t rise then?...
 
Yep Twin and earth for me as well, but I am interested to get the OPs idea regarding Flex, I would avoid it, but If I had to use it I would go 4mm2, that way I could charge the customer more :21:
 
I still can't understand the question, a 6mm2 T&E or a 2.5mm2 Flex, theres quite a difference in size here haha
no doubt it will be an existing supply mike....
and what they are wantin to know is if you have 6mm flat coming into the iso....is it ok to have 2.5 flex goin out....
i mean, all they have to do is look on a website for the max CCC for flex for christs sake....they`v got 20A OPD feeding this.....
beyond words...it really is.....
 

Reply to 2.5mm flex or 6mm t+e in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
356
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
909
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
This charger doesn't support rear entry from the looks, only bottom entry, hence that. Unless they make a white sheathed SWA, I would still need...
Replies
8
Views
1K
I would put this down to 433.3.1(ii) - no overload protection needed because the load at the single socket can't overload the cable, being fused...
Replies
14
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top