Hi

Im Looking for some advice on compliance as its a bit of a gray area

Kitchen currently has 13a FCU fed from ring main and 2.5mm lsf to single gang skt for washing machine.

Want to change this to

20a DP switch and spur off the single gang socket for washing machine and fit second single gang skt for dishwasher.

Reason for not fitting new FCU and separate supply is its a brand new house and would have to destroy tiles.

I realise the current capacity of the 2.5 is round 20a but the washing machine and dishwasher are no where near pulling that even with both heaters on at same time and taking diversity in to account would imagine it is unlikely to ever have both machines on the heating phase at the same time.

Would this be acceptable ?
 
Yes back in the day it was fine but I ain't been on the tools in a long time and not domestically.

So if its acceptable for an EICR to have a socket under the sink can it be fed directly from the ring via 2.5mm radial?
Yes, as long as it's a single or double socket, but if it's a double, the question arises as to whether it's acceptable to plug in two appliances with a combined intermittent draw that might exceed 20A.
 

Reply to 2.5mm lsf radial from 20a DP switch in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
361
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
921
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

"It works" and "it's safe" are not necessarily the same thing. With DIY work, they are often far from the same thing.
Replies
7
Views
728
  • Question
We just left it as it was, again the customer didn't seem too bothered, dont think she wanted me digging any further.
Replies
14
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top