R

Roger Perkin

I am building a garden office and currently have 25mm Celotex in the walls. I am running the ring main around and then want to add some more Celotex.

My question is how much of an air gap do I need to leave for the ring main?
 
It is not so much how much air gap as what is the drop in current carrying capacity. Which in the case of 2.5mm² drops down to 17a (ish) in insulation thus reducing from 54a to 34a. How much load do you think is going on to the ring final circuit. I would say ring main but we have a pet rottweiler who will get cross if we do, he is right though!
 
The ccc of the live conductors ( iz) should not be less than 20amps in each leg of the ring final circuit.
See regulation 433.1.1 and 433.1.204
 
Last edited:
Interesting will check that (again) but umm well if the 2.5 is doubled up how do you read that? as in yes its drops to 17a ish but as it is doubled up it is 34a yes? No? Maybe, don't know...
Any conductor in a 32/30A ring final circuit should not be rated at less than 20A.
 
OK so I need to ideally not leave any air gaps in the insulation but need to run the ring circuit in there - total load on the cable will be a laptop, 2 monitors, and a 1kw heater and iphone charger - that's it
 
I thought it had to be a ring. It was only another 4m of cable to run it back no big deal - but just need to find out if I can bury the cable in the celotex or if I need to leave air around it?
 
Im assuming your talking about running cable in the cavity? where you have inserted celotex?

There is a requirement in the Building Regulations 2000, Approved Document C, 2004 Edition, Section 5: Walls, paragraph 5.13 b state that no cables other than electricity meter tails are to be located in the cavity of an external wall.
 

Reply to 2.5mm ring main and Celotex Insulation in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
393
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
978
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Yep! Edit button was disabled by the time I seen it. Hopefully the 15m/15m clarified what I intended 😀
2 3
Replies
36
Views
2K
Joining the ends of the radials together to form a ring, and changing the circuit protection to a single 32A would solve the MCB overload problem...
Replies
8
Views
783

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top