S

solo2771

Just a quicky,
Lighting circuit supplied by 4 core swa has become overloaded.
Would there be anything wrong with splitting into 2 circuits and using the 4 cores for L and N and the steel armour for earth for both? all conductors would be identified with sleeving.
Otherwise new cable needs running under concrete.
 
you would have to be absolutly positive the SWA of the cable would mannage the simultanious fault current on both circuits. It would involve a lot of cals and as it is probbably a smallish cable i seriously dought it would.
I dont think it can be done so get the cutter out and start digging sorry
 
Agree with the above and have a read of 514.4.4 and table 51 no mention of sleeving being permitted for identification of conductors.


Chris
 
I don't think that there's a problem with several circuits sharing an earth provided the csa is rated for the largest circuit.
You would need to know the equivalent csa of the armoured.
 
you would have to work out worst case and make sure on a similtanious earth fault on both circuits the swa would take it.
Manufacturest details for SWA Kfactor from section 5 etc
 
According to 543.1.2 where a protective conductor is common to two or more circuits it's csa shall be calculated for the most onerous fault current and operating time in each circuit, or selected so as to correspond to the csa of the largest line conductor.
 
DEcided to get them to get the breakers out as they use them anyway and just putting another swa in, thankyou for answers and it is something I am going to look into at some point. My main concern with using armourings is on jobs I have repaired in past water has got into the armourings and they have rusted almost away even though they had decent external gland kits fitted.
 
billy In a true ballanced 3 phase no no need for a neutral at all anywhere else the Neutral is classes as a line conductor therefore has to be the same as all aother line conductor.

Reg 534.2
 

Reply to 2 circuits in 4 core swa? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
382
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
963
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

You would treat it as a TT installation.
2
Replies
29
Views
2K
A picture paints a thousand words so here's an SLD showing my installation and some annotations to show the proposed relocation of the DC...
Replies
12
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top