I just wanted to share my find from a small job today.

I was at my friends to do a couple of bits for him before he moves out and noticed his CU. all very neat TN-S supply, and the MET had 10mm bonding and earthing conductor all dressed nicely. Then i noticed the other MET with only 16mm from the incoming cable.
When i asked what was going on, he showed me a bit of 16mm that he found on the floor when he moved in and just left at the back of the cupboard. It used to link the 2 METs
The House had been without a proper earth for at least the 2years he had been there.
 
Doesn't surprise me in the slightest!
Checked out someone's house once, pulled on the Gas bond, it kept on pulling...yes, just a couple of feet shoved through the floorboards not connected to anything. It was relatively new as well.
 
i hope you refitted that bit of 16mm and then performed a Ze.

I had some 16mm on the van so i replaced the piece from the incoming cable with a longer piece so there is now only 1MET.

I have never heard or read of one, but just out of curiosity is there any reg or advisory against having more than one MET at a CU?
I cant think of a decent reason as to why not apart from neatness.

Tim
 
I had some 16mm on the van so i replaced the piece from the incoming cable with a longer piece so there is now only 1MET.

I have never heard or read of one, but just out of curiosity is there any reg or advisory against having more than one MET at a CU?
I cant think of a decent reason as to why not apart from neatness.

Tim
hope you did a Ze to confirm that the 16mm is in fact connected to the neutral in the head.
 

Reply to 2 MET's in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
328
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
855
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
975

Similar threads

This was posted this week, on topic ....... https://niceic.com/newsletter/omission-of-overload-protection/?dm_i=7G1W,7GCE,K4L2A,WHET,1
Replies
8
Views
712
People who claim to be plumbers... and tilers... New bath fitted and the drain is accessible from the side and there are isolating valves on the...
    • Like
Replies
0
Views
220

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top