I've been wondering....
There are two estates of bungalows near me, all built together, all with traditional system boilers with tanks and cylinder.
It seems to me that either the valve actuators work for many years, or on some properties they need regular replacement to the point I keep them in stock.
There are about 7 properties where they will routinely go through one in 12-18 months, even if I install genuine Honeywell heads.
Of late I've taken to manually operating the valve about 100 times before putting a new head on, and this does seem to on average extend the life of the head to about 2 years.
Does it seem reasonable to conclude that if they are regularly failing the issue is mechanical friction or limited valve travel and the motor is burning out ?
I'm considering if rather than just changing them I should say we'll try one new head and after that get a plumber in to change the whole valve body.
Any thoughts, similar experiences, wisdom?
There are two estates of bungalows near me, all built together, all with traditional system boilers with tanks and cylinder.
It seems to me that either the valve actuators work for many years, or on some properties they need regular replacement to the point I keep them in stock.
There are about 7 properties where they will routinely go through one in 12-18 months, even if I install genuine Honeywell heads.
Of late I've taken to manually operating the valve about 100 times before putting a new head on, and this does seem to on average extend the life of the head to about 2 years.
Does it seem reasonable to conclude that if they are regularly failing the issue is mechanical friction or limited valve travel and the motor is burning out ?
I'm considering if rather than just changing them I should say we'll try one new head and after that get a plumber in to change the whole valve body.
Any thoughts, similar experiences, wisdom?