i would gland into the metal CU as its extraneous conductive part, i can't find why you can't, you ask for help and just get mocked, i see why people say don't go on here

Your not being mocked...I just asked a question. I doubt the metal CU is an extraneous conductive part! If you are making it a TT system at the far end then you need to isolate the suppliers earth from this part of the installation.
 
Last edited by a moderator:
I'm getting the impression you shouldn't connect straight into the metal CU, which doesn't tie up with other advice i've been told, i'm trying to do the job correctly and have had a look in the book but couldn't find anything thats why i ask... thanks simon, didn't know those were available
 
I'm getting the impression you shouldn't connect straight into the metal CU, which doesn't tie up with other advice i've been told, i'm trying to do the job correctly and have had a look in the book but couldn't find anything thats why i ask... thanks simon, didn't know those were available

How come you want to make the remote end TT?
 
Your not being mocked...I just asked a question. I doubt the metal CU is an extraneous conductive part! If you are making the it a TT system at the far end then you need to isolate the suppliers earth from this part of the installation.

i meant the steel of the SWA not the metal CU, sorry

and where can i find this in the book please?
 
As its about 70 something metres away and will be cheaper to install 2 core as its 25mm

What is at the far end? Shed, garage, house, etc.

The price difference between 2core and 3core will be about £1 a meter so about £70. You will more than likely recoup this in labour/material if you don't make the far end a TT arrangement.

Is there anything extraneous at the far end?
 
Last edited by a moderator:
542.1.3.3
Where a number of installations have separate earthing arrangements, any protective conductors common to any of these installations shall either be capable of carrying the maximum fault current likely to flow through them or be earthed within one installation only and be insulated from the earthing arrangements of any other installation.
 

Reply to the thread, titled "2 Questions" which is posted in Electrical Wiring, Theories and Regulations on Electricians Forums.

Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Daily, weekly or monthly email

Back
Top