Hi folks.

I cut one of the cables on my ring circuit, attached the 2 now separate ends to a new 30a junction box, and then run 2 additional spurs from the same junction box, using 32a twin and earth, on the end of each of these new spurs is a twin plug socket with usb.

I did the work with my father in law, who’s an avid DIYer and has been doing diy for 60 years.

We did a really good job, cables cut nice, neat, secure, tested them, and all working.

Due to a rush to get the job done before decorators, I pre installed the new sockets and cabling, ready for the junction, and only then did I realise I should have extended the ring.....it was too late, I had sealed the walls up and could not get another cable in. We used a square 30a MK box, which had ample room for the cables.

These are bedside outlets, not for heavy consuming items.

Some forums and people have now put the fear of god in me that this is dangerous, however I have read mixed opinions (e.g. apparatly 1 spur from any point is the Reg, ok.....so I have 2 on mine, but is this really much different than if I added another junction 10 inches away for my second spur)

Is this really a concern to warrant me ripping it all back out?

It’s a good tidy job.
I know there’s regulations and partP......hindsight is a wonderful thing.

Views?
Many thanks.

[ElectriciansForums.net] 2 spurs from a Junction Box....worried?
 
The joint box can effectively be considered as a socket on the ring. Only one unfused spur should be taken from a single point on a ring circuit as prescribed in appendix 15 the fact that’s it’s informative bears no weight on the argument as says that the design shown fulfils the requirements of 433.1

View attachment 45067

Ok, but where in 433.1 does it preclude taking two spurs from a single point on a ring final circuit?

That's all I'm asking.

I can't find a regulation that precludes it, but I'm happy to be proved wrong because then I'll have learned something new :)
 
The joint box can effectively be considered as a socket on the ring. Would you take two separate unfused spurs from one socket outlet? Only one unfused spur should be taken from a single point on a ring circuit as prescribed in appendix 15 the fact that’s it’s informative bears no weight on the argument as says that the design shown fulfils the requirements of 433.1 and therefore that’s why the appendix is informative the diagram clearly shows one junction box on the ring with one unfused spur connected to it.
You cannot specify indefinitely which loads will be connected to a socket by current or future users of the installation for example it would not be unreasonable for electric heaters to be plugged into both sockets in a situation where the main source of heating was broken and still have two sockets to plug in straighteners hairdryers etc etc which could lead to the overload of the junction box.
Not to mention bad practice of ramming 4 connections into each terminal of the junction box.

[ElectriciansForums.net] 2 spurs from a Junction Box....worried?
 
There is none, and what has been done is fine, if slightly unorthodox. Lots on here quoting appendix 15 as having some god like status, but it's only a guide, hence uses terms such as 'this can generally be achieved by' I.e. follow this and you don't have to think, all will be well. Think outside the box and all will still be well, provided you've thought, not guessed! In this case the op might have guessed but got away with it!
 
Oh no let’s not start this again!

None of us with a brain cell would ever do it this way anyway, so even if it isn’t against the regs let’s just pretend it is?

Someone said they’d only ever do it like this if they absolutley had too - but I can’t even imagine a scenario which would make this even a viable option.

So...

I’m rewriting the regs. It’s now forbidden.

Can we end this discussion now? My eyeballs are bleeding.
 
Appendix 15 is informative, and it says if you follow this appendix, you will meet the requirements of 433.1. However, it is NOT prescriptive, there may be other means of meeting 433.1 that are not covered by this diagram.

You don't have to "ram" 4 connections into each terminal, nowadays many (most?) of us are using maintenance-free connectors (Wago, etc.) that have 4 or 5 terminals, and are rated to 32A or more.
 
Appendix 15 is informative, and it says if you follow this appendix, you will meet the requirements of 433.1. However, it is NOT prescriptive, there may be other means of meeting 433.1 that are not covered by this diagram.

You don't have to "ram" 4 connections into each terminal, nowadays many (most?) of us are using maintenance-free connectors (Wago, etc.) that have 4 or 5 terminals, and are rated to 32A or more.

Wago's are 24 A if my memery serves me correctly
 
There is none, and what has been done is fine, if slightly unorthodox. Lots on here quoting appendix 15 as having some god like status, but it's only a guide, hence uses terms such as 'this can generally be achieved by' I.e. follow this and you don't have to think, all will be well. Think outside the box and all will still be well, provided you've thought, not guessed! In this case the op might have guessed but got away with it!
It says “this appendix sets out options for the design for ring final circuits in household and similar premises in accordance with regulation 433.1.”
For once there isn’t any ambiguity in the regulations
 
Last edited:
Appendix 15 is informative, and it says if you follow this appendix, you will meet the requirements of 433.1. However, it is NOT prescriptive, there may be other means of meeting 433.1 that are not covered by this diagram.

You don't have to "ram" 4 connections into each terminal, nowadays many (most?) of us are using maintenance-free connectors (Wago, etc.) that have 4 or 5 terminals, and are rated to 32A or more.
I’m not just trying to be argumentative I genuinely believe that it isn’t allowed.
where does it say there may be other means of meeting 433.1? I can’t see that anywhere?
I think the OP was saying that he used the screw type junction boxes and that’s why earlier in the thread someone had raised about the junction box needing to be accessible.
 
Last edited:
Let me ask the question in another way...

You've just been asked to inspect the OPs property for an EICR and you find this junction box, it's been changed to a maintenance free one so that's no longer an issue.

How would you code the fact there are two spurs taken from the one junction box and what regulation would you quote to substantiate that coding?
 
Ok, but where in 433.1 does it preclude taking two spurs from a single point on a ring final circuit?

Very rare I disagree with your stance on electrics but I think your enterpretation based on if it doesn't say you can't do something in the regs then you can do it.

It doesn't say you shouldn't wire a banana form a junction box to a tomatoe in a ring final, does that mean you can.

433.1 says what you can do.
 

Reply to 2 spurs from a Junction Box....worried? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
959
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
yeah. i think so. Details here..... https://www.electriciansforums.net/threads/havent-seen-tel-for-a-month.210295/
Replies
14
Views
2K
  • Question
Ouch. Danger notice to customer in my book.
    • Like
Replies
1
Views
622

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top