Been to fit new led pir flood. 3core +e. Perm live. Sw live. N e.
Flood is 2core. So wired it perm live set up works a treat. Customer rings up wants it on switch. After investigating switch is a 2 way.. any way of doing this so works on pir then on with switch.
It's a sealed led light 2 core.
 
If you have only a line and neutral connection to an integrated sealed LED PIR light then you cannot have a manual ON switch as the wiring cannot bypass the PIR.
You can have a manual OFF switch, as you just switch the line to the light.

If you were to open up the LED light then you might be able to rearrange the wiring so that you have a connection direct to the LED and then with only a two way switch you would have to have it that the PIR sensor was disconnected whilst it was in manual ON, which would mean restarting the sensor once the switch was operated. This often causes the PIR to come on for a while!
 
Last edited:
If you have only a line an neutral connection to an integrated sealed LED PIR light then you cannot have a manual ON switch as the wiring cannot bypass the PIR.
You can have a manual OFF switch as you just switch the line to the light.

If you were to open up the LED light then you light be able to rearrange the wiring so that you have a connection direct to the LED and then with only a two way switch you would have to have it that the PIR sensor was disconnected whilst it was in manual on, which would mean restarting the sensor once the switch was operated. This often causes the PIR to come on for a while!
That was my thinking but don't want to open light up. Must have been a old halogen light that was fitted with perm live and sw live terminal or cut into pir / lamp circuit
 
Would my suggestion not work? So when the switch is on it feeds what would be the switched live of the PIR therefore powering the fitting? When the switch is off the PIR would work as normal?
If there were access to the switched line on the light fitting then it would work though with a 2 way switch the power to the PIR sensor would be switched off when the light is on manual.
[ElectriciansForums.net] 2 way switching pir led
However in this case there is no access to switched line to the light only permanent line to the PIR sensor.
 

Reply to 2 way switching pir led in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
702
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
3K

Similar threads

Thanks again for your help, now solved đź‘Ť
Replies
11
Views
848
  • Question
Interesting that Avo 8 has brought Legrand into the conversation, as it certainly could be done with the Legrand IP55 switches I've used for about...
Replies
13
Views
991

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top