First : here are 2 x sockets .What code would you give and why ? 3rd pick you can see rear thermal damage on double socket



second : Roof above bathroom has terrible leaks . Lights spark and buzz etc when raining .Video evidence shown to tester . tester says it not a C1 or C2 as its not raining despite the videos taken when it does .So as inspected its not a issue . Thoughts >??
 

Attachments

  • [ElectriciansForums.net] 2 x sockets : EICR . What would you code . Then another question !
    bf98ff10-a35d-4c49-8da8-60b032200d7a.jpeg
    86.4 KB · Views: 28
  • [ElectriciansForums.net] 2 x sockets : EICR . What would you code . Then another question !
    3d1d6333-6fdc-420a-8d34-20abf894b9dd.jpeg
    176 KB · Views: 29
  • [ElectriciansForums.net] 2 x sockets : EICR . What would you code . Then another question !
    06ff25ac-85fb-43e5-95fb-4289167ad9bc.jpeg
    448.9 KB · Views: 28
Last edited:
Already covered in BPG #4:

Fire/Heat - C2 - Evidence of excessive heat (such as charring from electrical equipment causing damage to the installation or its surroundings)

Replacement would appear to be the obvious course of action to anyone with half a brain...

As for the second issue I think this covers it in BPG #4:

Equipment/Accessories - C2 - Electrical equipment having an inadequate degree of ingress protection (IP rating) for the external influences likely to occur in the location, if this results in potential danger

But I think @littlespark has summed it up perfectly.
 
Tester said its not even a C3 !!
Its a "charity job" as usual . For a vulnerable person . So Ive given my report but also offered to "put it out there" so the other people helping her can see others opinion etc etc
 
Sockets are definite C2’s in my eyes.

With regards to the lighting issue, first and foremost she needs to get that roof fixed to stem the leaks, then a good inspection to see what accessories / wiring has water damage and needs replacing. C2/FI

And as above, sack the tester.
 
What is slightly curious is it appears to be the N pin in both cases that has burnt out, often when plugs go bad it is the L with the fuse that runs hotter. I wonder if they had an electric heater with a bad plug that was responsible for both?
 
If the lights spark and buzz when it rains.... what's an IR showing up during testing? Maybe everything works ok when its not raining, but it cant be bone dry.



EICR section 5, item 18...... (on my particular sheets anyway)
"Condition of accessories including socket-outlets, switches and joint boxes (651.2(v))"

Minimum C2. Maybe not "immediately" dangerous.... but its not going to take much for that to fail completely.
 
tester had an email .Reminding of BPG and also its an obvious C2 .And Perhaps he should concentrate a little better rather than trying to give a "nicer " report for the landlord who has a Council complaint been made against them etc
 
First : here are 2 x sockets .What code would you give and why ? 3rd pick you can see rear thermal damage on double socket



second : Roof above bathroom has terrible leaks . Lights spark and buzz etc when raining .Video evidence shown to tester . tester says it not a C1 or C2 as its not raining despite the videos taken when it does .So as inspected its not a issue . Thoughts >??
If the sockets are replaced than the test is carried out. There is no reason to put this in the certificate as any C code
 
Sockets are definite C2’s in my eyes.

With regards to the lighting issue, first and foremost she needs to get that roof fixed to stem the leaks, then a good inspection to see what accessories / wiring has water damage and needs replacing. C2/FI

And as above, sack the tester.
If the sockets have been replaced why would you list it.?
 
Welcome to the forum, @uc1987 and you bring up a very good point.

@LukeD, Were these sockets replaced?
I admit, I originally didn’t see the third photo showing the backs of them…. Had they been removed for replacement, or just removed, photo, and put back on?

I suppose the other issue, it can be argued that there was no fault on the lights “at the time of the test”…. But I would still think there would be signs of dampness under an IR test.

Maybe low, but not low enough to say it’s a fault?
 

Reply to 2 x sockets : EICR . What would you code . Then another question ! in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar threads

In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...
Replies
11
Views
2K
Hello Ric2013, MJPD29 and westward 10. I have a multimeter that I tested the voltage with and before I open the socket up I use a plug in tester...
Replies
4
Views
1K

Recommended Sponsor News

  • Article
thanks for the clarification. ( also thanks to Dan. ).
Replies
6
Views
2K
  • Article
More info on link below http://sbsc.uk.net/
    • Like
2
Replies
22
Views
9K
  • Article
Happy Friday Everyone! Subscribe for more jokes direct to your mailbox or send us your own jokes to be in with a chance of featuring, by clicking...
    • Like
2
Replies
27
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top