Hi all,

1st fixing a barn conversion at the mo


Builder has threw a spanner in the works and says the location of fan will now be in zone 1 near shower.

If it has to be selv then i will wire for a transformer. only snag is i allowed for standard fan and selv fan is a *** load more lol

the OSG says though minimum IPX5 with water jets and i was looking at this unit

XPELAIR DX100BT 100MM AXIAL BATHROOM FAN WITH TIMER. Free delivery! | eBay

what you reckon?
 
As an eBay Associate we earn from qualifying purchases.
230V ventilation gear is allowable in zone 1 as long as it is at least IP44 and the manufacturers instructions don't state that it isn't suitable for use in zone 1.

Double check your instructions and then carry on as normal.

Can no one read a book these days? It's written in black and white in section 701!
 
230V ventilation gear is allowable in zone 1 as long as it is at least IP44 and the manufacturers instructions don't state that it isn't suitable for use in zone 1.

Double check your instructions and then carry on as normal.

Can no one read a book these days? It's written in black and white in section 701!




I referred to the OSG 1st as it's always to hand in the van

thanks for all comments


cheers
 
230V ventilation gear is allowable in zone 1 as long as it is at least IP44 and the manufacturers instructions don't state that it isn't suitable for use in zone 1.

Double check your instructions and then carry on as normal.

Can no one read a book these days? It's written in black and white in section 701!

Hi D,
While that is true, a note accompanying that paragraph (GN7) states where the equipment is to be used where water jets are present (in that zone) then they shall have a IP of at least IPX5

Also no one has mentioned where Selv/Pelv fans are concerned the safety supply source shall be fitted outside of the zones.
 
Last edited:
Well if anyone is going to install a mains fan in a water jet then they're a moron! Lol. The only place where you're going to fit a fan is either on the wall or in the ceiling at a height above the shower head, in which case, IPX4 is all it needs be.
 
Well if anyone is going to install a mains fan in a water jet then they're a moron! Lol. The only place where you're going to fit a fan is either on the wall or in the ceiling at a height above the shower head, in which case, IPX4 is all it needs be.

Would you class a shower head with a removable hose as fixed though?
 
You can never tell on here Dilb lol (conversation re: 150m spur last night lol)

Here is the page D, you may interpret it differently to me, just I had a similar argument with a builder, I ended up fitting a Selv Fan lol
 

Attachments

  • 001.pdf
    1.7 MB · Views: 1,639
  • [ElectriciansForums.net] 230V fan in Zone 1?
    001.jpg
    116.5 KB · Views: 50
Well that''s down to interpretation, as it says IPX4 unless it is likely to come into contact with spray e.g cleaning. Now how many people up and down the country would not use the shower head to clean the tiles down? Not saying they will spray directly at the fan but near to it.
 
The fan identified in the OP is listed as IPX5 and so is suitable for use in zone one and in an area with water jets.

The thing to remember about water jets is that they are meant to be powerful and the spray head of a standard shower is not considered a water jet.
IPX4 means it can cope with splashed water from any direction so theoretically playing a shower on an IPX4 item should be safe ( I wouldn't risk it).
If you start considering the mobile spray head as the location of the shower then most of a small bathroom would be zone 1! It is the fixed outlet that is of relevance to the regs.
 
As you say, it boils down to interpretation, and what you are comfortable signing your name to.

IPX4 protected from water splashing for all directions

IPX5 protected from low pressure jets from all directions

IPX6 protected from high pressure jets from all directions

It is up to whoever is signing the paperwork to decide what a shower is classed as, not to really prove anyone is right or wrong, we will all have our own take on it.











 
To be fair I am not really comfortable fitting 230V fans in zone 1, particularly if it can be sprayed with the shower (kids might find that funny and a great game), so I would prefer to fit Selv, or if it really had to be 230V then IPX5 (unless the manufacture stated a particular type @ IPX4 was suitable for zone 1).

This is just my interpretation of things, and my personal opinion, others may well decide differently, me ? I prefer to err on the side of caution.
 
Last edited:
1 Protected against vertically falling drops of water (condensation)
2 Protected against drops of water falling at up to 15 deg from the vertical
3 Protected against drops of water falling at up to 60 deg from the vertical
4 Protected against splashing of water from all directions
5 Protected against jets of water from all directions (12.5 mm core nozzle, 10 m head at 3m distance)
6 Protected against jets of water from all directions (12.5 mm core nozzle, 10 m head at 1.3 m distance)
 

Reply to 230V fan in Zone 1? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
From looking at a picture there is no way of knowing, an electrician can carry out some simple tests.
Replies
12
Views
5K
  • Question
Then we can all rest easy; after all, if the IET say its fine, manufactures say its fine, who are we to suggest otherwise.
2
Replies
30
Views
3K
S
Re: What is the current 17th edition regs for 12v SELV Humidisat extractor fans in Zo The chicken & egg aka the PYRO or the gas mains conundrum...
Replies
21
Views
5K
sintec
S
  • Question
Hi cheers for all replies There is a existing fan so drilling another hole would be out of the question as from the outside the grill isnt...
Replies
17
Views
8K
T
  • Question
Most inline axial fans are terrible, any axial fan that has lengthy ducts of turbulent inducing flexible ducting has been poor when I've tested it...
Replies
52
Views
78K
vambo
V

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks