Somewhat odd advice perhaps, I must be missing something.So I have asked them for some guidance:
- Calc CPC size using selected Circuit Breakers Zs.
- Then work out R1+R2
- Select cable from Table I1 to meet minimum R1+R2 value.
- Once the cable is selected, work out actual R1+R2 and calculate actual circuit Zs - including correction factors 1.20
- Calc to confirm actual CPC size using Adiabatic Equation.
- Circuit length needs to be greater than 15m.
I can only think they mean determine cable size from breaker size and Zs
R1+R2 maximum value is straightforward
Minimum cable size to meet breaker rating would work, and then compare to required R1+R2.
Then with cable selected R1+R2 and Zs is OK
Adiabatic not without more information or using the 80A and 0.1s values.
Not sure where the circuit length comes into it.