Just sat this tonight. What does everyone that sat it tonight think of the paper?
 
Votage drop calculation formula= R1 + Rn x 1.2 x Ib
So in this case = 0.38 x 1.2 x 30
Voltage drop = 13.68v = 5.95 % DOES NOT COMPLY!!

1.2 is the multiplying factor to convert the resistance of a copper conductor at a temp' of 20 degrees C to a temp' of 70 degrees C.

The question gave resistances of R1 and Rn but did not say at what temperature. So why are you using 1.2 ??
 
Upvote 0
1.2 is used because you have to take maximum operating temp of the cable when making this calculation. Otherwise when the circuit is in use and the temp of the cable rises the calculations and current carrying capacity will change. Worst case Scenario. Otherwise it would comply when not in use but possibly not when in use.
 
Upvote 0
1.2 is used because you have to take maximum operating temp of the cable when making this calculation. Otherwise when the circuit is in use and the temp of the cable rises the calculations and current carrying capacity will change. Worst case Scenario. Otherwise it would comply when not in use but possibly not when in use.

1.2 is used to convert a 20 degree resistance reading to a 70 degree resistance reading. See p105 of GN3:

For examplea reading taken at 20 degrees C could be converted to an equivalent reading at 70 degrees by determining the correction factor obtained from p105:
(1 + 0.004 (amb temp - 20))

= 1 + 0.004 (70 - 20)

= 1 + 0.004 x 50

= 1.2 So this is the multiplying factor to convert 20 degrees C to 70 degrees C.

BUT THE IMPORTANT THING IS THE QUESTION DID NOT SAYWHAT TEMP THE READINGS OF R1 & Rn WERE TAKEN AT.
 
Upvote 0

Reply to 2391-10 Written Exam - 01/12/11 in the Electrician Courses : Electrical Quals area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
299
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
282
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
355

Similar threads

  • Question
Yeah I did think this. Once again. Thanks for all your help.👍🏻
Replies
4
Views
1K
  • Sticky
  • Question
Best Electrical Courses I endeavour to create a "best electrical courses" thread for 2025 (so training courses that did well during 2024 are the...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

  • exceeding voltage drop
    The cable is way undersized. If the voltage drop is detrimental to the installation I would make...
  • TT advise
    OK My take on the precautions to implement when omitting an up front RCD on a TT system. Tails...
  • SIL vs ATEX
    Good morning all, I have a question for those who are CompEx and SIL aware - I have various Ex...

Electrical Courses

This is the main Electrical Courses at ElectriciansForums.net. Find local recommended electricians courses. Avoid training "company" scams. Always go view the training centre before booking any electrical courses.
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top