2391-20 cable calcs
S
shambock
Hi
Anyone help with some cable calcs for my designe project, i must be missing something here.
Im trying to work out and show my calculations for cable sizing of a 32A ring
Length is 78 M
Number of 13A double sockets is 7
Ib is 32A
In is 32A RCBO
It should be In / Correction factors of wich i only have a grouping factor of 0.41
This makes it 32/0.41 = 78A
The above formula say that i should be using a cable capable of carrying 78A wich brings it upto 25mm ????????????? (ref meth B,singles) table 4D1A.
I know this is wrong but where am i mucking up.
Please help
I'm not sure what you are trying to do exactly but you will have to change the derating factor by choosing another installation method.
Are the circuits all 78m run together? Move the db or have an additional one nearer.
Upvote 0
Ring circuit cable tabulated rating (It) formula
In BS7671 the rules are changed for the special case of the 30 and 32 A final ring circuit (Regulation 433.1.5), where overload protection requirements are amended allowing 20 A rated cables (Iz > or equal to 20 A) providing the load current in any part of the ring is unlikely to exceed 20 A.
Therefore Iz > or equal to 20 but Iz = It Ca Cg Ci Cc
Hence It > or equal to 20/(CaCgCiCc)
Example
A ring final circuit wired in thermoplastic (PVC) cable a sper Table 4D5 enclosed in conduit in an insulated wall and protected by a 32 A circuit breaker (In = 32 A); the cable rating must equal or exceed 20 A. The cable rating,
It > or equal to 20/(CaCgCiCc) if Ca = Cg = Ci = Cc = 1 then It > or equal to 20 A
From Table 4D5 (column 7) a 2.5mm cable is therefore adequate.
Upvote 0
Are yours and all these other 16 circuits operating at full load currents?? Now, there's a little clue for you ...lol!!!
Upvote 0
Widdler. an excellent response. But how do we proceed given that the OP had specified that the circuit be run in singles, ref method B. does not table 4D5 not apply here as that's for twin and earth?
Upvote 0
'54, how do you apply diversity to this situation (i take it that is what you are implying?) OSG states that diversity to socket outlets 10 A then 50% in domestic.
It's a confusing scenario, with not enough detail, granted
How then do I find myself pulling many meters of many circuits into sometimes 6" trunking on runs in schools etc..?
Upvote 0
i was just giving an example.
its not too hard to adjust the data to suit the OP's scenario.
Upvote 0
I take it that from your correction factor of 0.41, that you have 6 circuits in the trunking?
This is a RFC, which means that there are two conductors in parallel, the correction factor should be doubled.
Which would give you a conductor size of 6mm².
Upvote 0
6 or 16??
OP, TBH if there is this large number i can't see how this can be calculated without at least some indication of what the expected load is and whether it will be evenly distributed - is this for some commercial or industrial premises? Is installing submains not an option? Is it 3 phase or single phase?
Why so many circuits?
If it is domectic premises table 7.1 in the OSG gives guidance on ring main length with various PDs.
:confused:
Upvote 0
6 or 16??
:confused:
I am taking the area of the trunking where most circuits will meet ie right above the DB in question, i can get it down to 12 circuits but am unable due to cost run seperate circuits in seperate tubes thus removing correction factors all together.
The lighting and fixed power outlets eg 4.2KW dishwasher have been done and compleated by me but the ring is proving difficult due to the fact i have no idea what will be plugged in.
Upvote 0
This might be of use to you - If your lighting circuits are operating at less than 30% of the capacity for their cables they can be ignored from the total number of circuits when working out the rating factor for grouping see note 9, P126 OSG or P268 of BS 7671.
Also if your cables are more than 2x their diameter, horizontally apart from others then their rating factor can be ignored. eg if you had 10 cables and you cable tie them in 2 groups to opposite sides of the trunking with sufficient space between them then they can be counted just as 5 circuits (see note 2) :)
Upvote 0
Surely, If there's room to do this, then then leaving them loose would not warrant the 0.41 derating factor in the first place?
Upvote 0
shambock,
johnboy6083,
Electrical Courses