A single phase power circuit supplying an item of equipment,having a full load current of 25 A,is to be checked to confirm voltage drop compliance.The circuit is installed using 6.0 mm2 cooper conductors,with a circuit length of 35m.
a) Calculate the maximum permissible voltage drop for this circuit.

b) The line and neutral combined resistance for the circuit is 0.26 Ohms . Determine whether the circuit meets the voltage drop requirements if the voltage drop to the local distribution board 4.5 V.

c)State one other method which could be used to confirm voltage drop.
 
A/ The equation is mv/m x Ib X length / 1000

What is the method of erection as in the 2391-10 or 20 they will give you this as the mv/m differes between method


B/ Reading the question means ( I think ) U= I x R where U is the volt drop, R is the resistance and I is the load so in your circuit

25 x 0.26 = 6.5 volts so therfore you 4.5 volts are acceptable


C/ U = I x R

Fingers crossed
 
L and N combined is 0.26. should we not use res.of L only to determine volt drop, i.e.0.13?
 
A) Is asking for the maximum permissable voltage drop which is 5% for circuits other than lighting so equals 11.5 Volts

The other method for me, would be measurement.
 
Last edited:
ywah, i saw that and thought stupid question how do you calculate permissible volt drop when it's set in stone as 5% ( 3% if lighting). trick question or badly worded.
 
No mate you use both

Sorry didn't see the IQ post pesky Arsenal supporters.

Lol, so you take your calculated volt drop for the sub circuit, add it to the volt drop given at the DB and if the total is less than 11.5 Volts, the circuit meets volt drop requirements.

Oh Arsenal we love you....
 
of course, silly me. the table values of mV/A/m are dependent on the length of the circuit, there and back, if you like. but the actual volt drop is at the point of utilisation.
 
of course, silly me. the table values of mV/A/m are dependent on the length of the circuit, there and back, if you like. but the actual volt drop is at the point of utilisation.

And that caught out many taking the June 2010 2391-10 exam, the conductor resistances were given, not the tabulated values from the reg's.
 

Reply to 2391 exam question. pls give an answer in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
296
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
804
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
840

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top