Are you using 1.2 as a temperature correction factor when ambient temperature is not given?
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss 2391 exam question. pls give an answer in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
1.2 because its the multiplier
Why do you measure resistance of both L and N when calculating volt drop? I thought the purpose of establishing if volt drop is in acceptable limits is to ensure that equipment will receive adequate voltage/current to function correctly. So we ought to then only be concerned with volt drop between CU and the load, not from CU then through the load and over the complete return path.
no 1.20 because the resistance value is at 20 degree C , and when vd occurs its under load so at a given temp of 70 degree C
I've never done a voltage drop calculation using the 1.2 factor, this assumes a fully loaded circuit at maximum operating temperature, a scenario so rare that even the IET's own Design Guide book does not consider it necessary.
because if at DB1 you have 230V and at DB2 you have a 4.5 VD and then another 7.6 V at the end of a circuit fed from DB2 then the total VD is now 12.1 v
1.2 is correct when using resistance at 20 degrees though , are you using the other method where you times the length and IB and mv/m ?
which is different to the figures in table 9a
I've never done a voltage drop calculation using the 1.2 factor, this assumes a fully loaded circuit at maximum operating temperature, a scenario so rare that even the IET's own Design Guide book does not consider it necessary.
And that caught out many taking the June 2010 2391-10 exam, the conductor resistances were given, not the tabulated values from the reg's.
Yes, for exam purposes, you need to use the 1.2 factor but I'm talking about my design calculations,.
-If I have a cable with a CCP of say 87 Amps, my Ib will be well below this level and as a result, my conductor operating temperature will be nowhere near maximum
It's the difference between a rigid factor and some real world commercial acumen/experience to supplement the regulations
"Where it is known that the actual operating temperature under normal load is less than the maximum permissible value for the type of cable insulation concerned (as given in the tables of current carrying capacity) the multipliers given in Table 9C may be reduced accordingly"
OSG Page 167
Sorry, I still don't get it. I see no reference to a sub-board in the original question, and even if there was, surely the VD will only be along the L that supplies the sub-board. I still don't see how VD along the neutral comes in to play.
if it didn't then we could do away with it and just use single core cable.Does current flow in the neutral in a single phase circuit?