View the thread, titled "2391 question" which is posted in Australia on Electricians Forums.

i=p/u

-
Arms
have 400/230v supply tn-c-s system with 35mm supply conductors..(ze 0.1 ohms) there is an extension built which is a 30m run of 3 core swa with 25mm conductors, one core is used as circuit protective conductor

Q , state giving reason wheather the copper cpc incorparated in distribution circuit is suitable as part of the main equpotential bonding to gas and water services installed to the new building from public supply

Q, descibe a suitaqble test to confirm the continuity of cpc in distribution cable
 
Last edited:
In general, the greater the area of insulation there is, the lower the resistance.
As such all of the answers should be 'increase'.
 
I think you will have to decide yourselves.
Consider why insulation resistance would decrease, then apply it to the various scenarios in the question.
 
RCD question

b) 200mA
c) 300ms

only 30mA (or less) RCDs used for additional protection are tested @ 5X I delta n

general purpose RCD to BSEN 61008 max = 300ms

general purpose others max = 200ms

Spark, where did you get this information from regarding testing at 5X ?
And the 300ms for BSEN61008, all others at 200ms ?
 
Hi Ringer,

general purpose RCD to BSEN 61008 max = 300ms

general purpose others max = 200ms

This is in the OSG, but excludes S types and the types which are 30mA or less which trip in the 40ms required @ 5 X I delta n for additional protection.

Spark, where did you get this information from regarding testing at 5X
This is also in the OSG, but I got the info. from elsewhere, which escapes me at the minute.

red OSG (cos I haven't got the green one yet) pages 91 and 92 sections 11.2, 11.3, 11.4 and 11.5
 

Reply to the thread, titled "2391 question" which is posted in Australia on Electricians Forums.

Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Daily, weekly or monthly email

Back
Top