2391 question | Page 2 | on ElectriciansForums

Discuss 2391 question in the Australia area at ElectriciansForums.net

i=p/u

-
Arms
Joined
Dec 9, 2010
Messages
7,520
Reaction score
816
Location
Northern Ireland
have 400/230v supply tn-c-s system with 35mm supply conductors..(ze 0.1 ohms) there is an extension built which is a 30m run of 3 core swa with 25mm conductors, one core is used as circuit protective conductor

Q , state giving reason wheather the copper cpc incorparated in distribution circuit is suitable as part of the main equpotential bonding to gas and water services installed to the new building from public supply

Q, descibe a suitaqble test to confirm the continuity of cpc in distribution cable
 
Last edited:
You mean assuming the conductor has enough capacity to do both jobs? To be honest - I can't think of a regulation that specifically forbids it. But I would have thought it would be bad practice. And as stated in an earlier post by yourself, circulating currents may generate enough heat to affect the other conductors in the cable. Is that not why bonding cables are usually run separately from all other circuits?
 
hi spin As for the circulating neutral currents, I don't think they care what the conductor is called, if it's there and it's connected, they'll use it.

i am only going with what is prescribed in gn 8
 
but if the 25mm condutor is going to MET how does this reach the extraneous conductive parts... probably thinking to hard now, thanks wise ones, later and thx


i think thats why there is a high fail rate on the 2391 cos some times the questions are poorly worded and people are unsure what they are looking for as an answer
 
You mean assuming the conductor has enough capacity to do both jobs? To be honest - I can't think of a regulation that specifically forbids it. But I would have thought it would be bad practice. And as stated in an earlier post by yourself, circulating currents may generate enough heat to affect the other conductors in the cable. Is that not why bonding cables are usually run separately from all other circuits?

if you look at gn 8 page 52 it shows a pme supply to a separate building using the cable as a combined cpc and bonding conductor as illustrated

also worth noting is when your maximum zs can not be meet you can use supplamentay bonding to achive this
 
Last edited by a moderator:
15. An earth electrode resistance test has been carried out, and the following results were obtained: 128Ohms, 120Ohms and 134Ohms. Determine the value of RA to be recorded on the certificate. Show all calculations.

il get by with a little help, ty

id say add them together and divide by 3 to get awnser... i dont think it wants you to go into the effectiveness of the values given..help help i think
 
10 State the effect each of the following would have on the measured insulation resistance of a conductor.

a) decrease in length increase

b) decrease in CSA none

c) decrease in temperature none




 
Last edited:
Why do you believe that a decrease in conductor length will result in a decrease in insulation resistance?
What do you believe causes an increase or decrease in insulation resistance?
 
Last edited by a moderator:
19 A 200mA general purpose RCD to BSEN 61008 is to be tested to ensure it operates within specification. State the

a) test instrument to be used rcd tester

b) the maximum test current to be applied during the test 500mA

c) the maximum acceptable tripping time during the test in b) above 40ms min 150 max

 
Last edited:
RCD question

b) 200mA
c) 300ms

only 30mA (or less) RCDs used for additional protection are tested @ 5X I delta n

general purpose RCD to BSEN 61008 max = 300ms

general purpose others max = 200ms
 
Last edited:

Reply to 2391 question in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
300
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
812
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
869

Similar threads

  • Question
He is after the four options for 1 and 2 of the multiple choice exam, probably optimistic someone will know this. Your question 3 in incomplete to...
Replies
2
Views
1K
  • Question
As you have actually measured the cold resistance (R1 + Rn = 0.15) then you have the voltage drop at the expected current (60A) so you can compute...
Replies
2
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top