2391 | on ElectriciansForums
Guest viewing is limited
Discuss 2391 in the UK Electrical Forum area at ElectriciansForums.net
sparky71
Sat my 2391 in aug got the results back over the phone failed
Did not say what area I failed on
Is there any way to revise and remember all gn3
Hi sparky71 sorry to hear this.......I can help you if you want to pm me some stuff you think you may of struggled on and maybe give you some guidance on stuff that will Probably pop up......I didn't even look at GN3 and I passed it and know I would pass it every single time.
First of all can you remember whereabouts you struggled?
Right ok well on mine I had a earth fault loop diagram.......that you can get say 11-12 points just for drawing it
Then I had a IR test
Bullet point the whole procedure.
Warning signs
Warn people of test carrying out
Isolate and lock
Sensitive equipment removed & linked out
Etc etc
Then at the end check results against bs7671 to make sure comply then reinstate circuit to original condition ......there's 2 extra points at the end
Then I had a test sheet there was like 7 zs results that were below the maxium stated but not within 80% of so they were flagged, then there will always be a IR of like 0.23 n-e with say 299 either side of it, just watch out for them.
The earth electrode test popped up on mine that's a GN3 thing as hard to explains on here you would need the illustrations.......15 marks again rekon I proble got about 7 on that as I don't know that fully which I regretted when I left the exam!
I would say Somthing like this......
Put up warning signs and warn people I testing
Dead test so safe isolation and lock off
Check machine complies with gs38 ....2-4mm tip, finger guards, inline fuses, 1000v insulated leads, no defects on machine, calibration certificate.
Then set machine on the low ohms scale
Null your test leads out or take reading of leads and subtract from result. (would just stick with null)
Prepare conductor for test.
Take end to end reading of line, & nuetral they should be withing 0.05 Then the cpc reading should be 1.67 times greater.
Then cross over the outgoing Nuetral to the incoming line and vice versa. And take the results at each point o the circuit to ensure no loops etc again they shoul be withing 0.05
Then do the same with your line & earth and test at each point the highest reading should be the one recorded, if a result is particularly higher then this will be a spare wired that result shoul be recorded.
Reinstate circuit to original condition and proceed to next test.
Should get close to maxium marks for that
Reply to 2391 in the UK Electrical Forum area at ElectriciansForums.net
The coding part is all down to experience and knowing whether something is right or wrong. Remember some pics have no faults.
My older card has it but my newer card doesn’t
Recommended Sponsor News
Hi everyone,