hello,
studying for my 2396 exam and i need some help!
Been banging my head against a wall for hours trying to get this one straight in my mind.
The question is as follows:
An electrical installation within a small retail outlet, located in a farm building is to be designed with the protective measure of ADS. The supply and installation form a 230V singles phase TT system. All wiring systems are surface mounted Ra(Ze) 12 ohm and PFC 2.1Ka
A) Answered this
B) one of the circuits is protected by a 32A 30mA RCBO and the circuit is wired using 4mm2/1.5mm2 flat profile cable to a length of 17m.
Determine if this circuit has adequate,
I) Earth fault protection
work out Zs and then a 32A has an max Zs of 1.37 assuming Type b but with the RCBO should it be 1667? just so confused
II) Short circuit protection
Dont know where to start
Any help would be greatly appreciated. just point me i a direction.
Dan
studying for my 2396 exam and i need some help!
Been banging my head against a wall for hours trying to get this one straight in my mind.
The question is as follows:
An electrical installation within a small retail outlet, located in a farm building is to be designed with the protective measure of ADS. The supply and installation form a 230V singles phase TT system. All wiring systems are surface mounted Ra(Ze) 12 ohm and PFC 2.1Ka
A) Answered this
B) one of the circuits is protected by a 32A 30mA RCBO and the circuit is wired using 4mm2/1.5mm2 flat profile cable to a length of 17m.
Determine if this circuit has adequate,
I) Earth fault protection
work out Zs and then a 32A has an max Zs of 1.37 assuming Type b but with the RCBO should it be 1667? just so confused
II) Short circuit protection
Dont know where to start
Any help would be greatly appreciated. just point me i a direction.
Dan