solo2771
why fp 200?
why fp 200?
What if each light is fused down through a connection unit?16A is the maximum you can have on a lighting circuit under the 17th
Checked the SQ-D mcb tech' section, if you have a 16A (D) then the max is 4 * 400w metal halides.
All the mcb brands usually sing a similar tune, making this a type (c) or (b), increasing the no' of lamps or decreasing the mcb rating will all make you prone to nuisance tripping on start up.Note using to type (d) will limit your allowable ELI dramatically so take this into account when running long runs.
It doesnt calculate like that its what the mcb's inrush can withstand with multiple inductives loads and this doesn't calculate uniformly thats why you need to pick your method then refer to the tech on your brand of mcb.so 8 x 250 W on a 20 should be about the max, Still don't fancy all that conduit work