Toad
My electrician says he can't sign off the installation in my new loft conversion because the 240V extractor fan is in zone 1 (directly above the shower), and hence violates the Regs. He says the easiest option is to replace it with a 12V one, and locate the transformer remotely.
Disappointed, I phoned Vent Axia and Manrose to find out what 12V fans might be suitable, explaining my predicament. They both said the 240V fan is permitted in zone 1 under the 17th Edition Regs, provided the fan is IPX4 rated (which it is) and also that the circuit is RCD protected (which is it, since I have RCBOs on all circuits).
Please can someone confirm one way or the other. I don't want to embarass the electrician (NICEIC qualified), or myself, so I need to have reliable information on this, but obviously I don't want to change the fan if I don't have to!
Disappointed, I phoned Vent Axia and Manrose to find out what 12V fans might be suitable, explaining my predicament. They both said the 240V fan is permitted in zone 1 under the 17th Edition Regs, provided the fan is IPX4 rated (which it is) and also that the circuit is RCD protected (which is it, since I have RCBOs on all circuits).