yeh but is it a circuit or just a piece of cable? Where is the loop hah!
Well if it ain't a circuit how does current / fault current flow in it? Being creative, I'm thinking it's a >32A distribution circuit with a 5 or 1 sec disc time from 411.3.2.3 or .4 - at least it would be if I'd done it in 10mm :)
 
To the op I don't know the task you are undertaking but the EFLI or R1+R2 for the circuit from the house will be between the line conductor and armour of the cable which has been rendered inaccessible. This is the fault path for said circuit and has nothing to do with the TT arrangement. Whatever you are doing you will have to note the reading as Not Verified with the reasons.
 
He is trying to verify earth continuity to the armour of the cable which is not accessible as it is contained within pvc conduit to isolate it from the TT, this earth continuity is applicable to the circuit from the house and nothing to do with the TT.

Spot on.

Appoligise to everyone else for confusion.

Pete, duly noted.

The swa has been stripped back and the 2 cores run inside pvc conduit.

I did a board change after the customer had an EICR report conducted. This wasn't highlighted and only became apparent when I begun testing after the new consumer unit was installed.
 
Thanks,

I have put LIM in the box and noted on the EIC.

They also pulled 2 strands from the other swa (another circuit) and connector blocked it and used as the cpc :/ no idea why they never glanded properly.
 
Wilko has interpreted what I was getting at lol
Exactly as Wilko said ,don't know regarding the position of the RCD however you will need loop reading /Ze +(R1+R2) to determine that the protective device for the sub-distribution circuit will operate within the maximum time for example if someone should accidently put a spade into the cable.
 
To the op I don't know the task you are undertaking but the EFLI or R1+R2 for the circuit from the house will be between the line conductor and armour of the cable which has been rendered inaccessible. This is the fault path for said circuit and has nothing to do with the TT arrangement. Whatever you are doing you will have to note the reading as Not Verified with the reasons.
Will it have any reference to the choice of OCPD? cant see how as it's not being used as a cpc?
 

Reply to 2core swa, not earth load end.. TT in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
382
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
963
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

You would treat it as a TT installation.
2
Replies
29
Views
2K
Sounds more positive.
Replies
8
Views
632

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top