Well if it ain't a circuit how does current / fault current flow in it? Being creative, I'm thinking it's a >32A distribution circuit with a 5 or 1 sec disc time from 411.3.2.3 or .4 - at least it would be if I'd done it in 10mmyeh but is it a circuit or just a piece of cable? Where is the loop hah!
The MCB in the house protects the cable. The circuit in the garage is separate imho.how does current / fault current flow
He is trying to verify earth continuity to the armour of the cable which is not accessible as it is contained within pvc conduit to isolate it from the TT, this earth continuity is applicable to the circuit from the house and nothing to do with the TT.
Exactly as Wilko said ,don't know regarding the position of the RCD however you will need loop reading /Ze +(R1+R2) to determine that the protective device for the sub-distribution circuit will operate within the maximum time for example if someone should accidently put a spade into the cable.Wilko has interpreted what I was getting at lol
The LINE (live) conductor SWA via the substation etc.yeh but is it a circuit or just a piece of cable? Where is the loop hah!
Will it have any reference to the choice of OCPD? cant see how as it's not being used as a cpc?To the op I don't know the task you are undertaking but the EFLI or R1+R2 for the circuit from the house will be between the line conductor and armour of the cable which has been rendered inaccessible. This is the fault path for said circuit and has nothing to do with the TT arrangement. Whatever you are doing you will have to note the reading as Not Verified with the reasons.
Ok so you verified a piece of cable.The LINE (live) conductor SWA via the substation etc.
Yes and I then can confirm it is safe to energise in the new consumer unit should there be a fault with the sub-distribution circuit the C.P. device will operate.Ok so you verified a piece of cable.