Hello currently rewiring a flat. They have ask for us to install electric panel heaters.

Now I have not really done many be for. The ones I have done I have always ran then from there own cct on a 16a mcb (3kw)....


They have asked for 2 kw heaters in each room. How many of you would put two 2kw heaters on one cct from a 20A mcb. Load would be 17ish amps .

I don't see a problam with it. Before you all say we need more info. Total run 10m... Ran in massonary, so clipped direct.

Or would you just run each heater of it own radial ??
 
The worry is the overall load as mentioned, forgetting that for 2 seconds, if it was just 2 heaters only then you would be safe at 2 heaters on a 4mm2 cable on a 20 amp MCB, even allowing for insulation etc it would be more than likely adequate, but now getting back to potential load, as you have mentioned there will be 2 in each room, how many rooms are there?
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
2kw heaters
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
9
Unsolved
--

Advert

Thread statistics

Created
james king,
Last reply from
MDJ,
Replies
9
Views
17,716

Advert

Back
Top