Sounds like a non sensicle installation. 100A RCD feeding 63A RCD all 30mA instant... Why? you have discrimination issue immediately. The second MCB seems to serve no purpose - could just be a MCB.
200 odd MOhms is a perfectly acceptable value, so not sure how you can claim that to be the fault when clearly so many other issues seem to exist. Do the maths, and you'll see why it's not going to be an IR value of 200M that's causing a 30mA RCD to trip.
Do you have an IR tester? as what you are discribing could well be an underlying low resistance that on its own is not enougth to cause a tripping situation, but when a suden increase in load is seen it unbalences the RCD. (this is very common)
Correct! You know your stuff mate! #cheers
Reply to 3 63 amp RCDs on same circiut in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Yes I touched on diverted neutrals when I went over guidance note 3 the first time but I’m doing a second round and going between all books whilst...
Regulations notwithstanding, the only thing in those pics that is likely to be affected by sheep is the trailing flexibles on the ground from the...