3 time 63 amp. equal 189 amp. overload if use only one phase. voltage drop is another problem.
 
It’s not likely to be a conventional fault given the situation. My best advice is contact Paul and take him up on his offer. Given the situation the dangers to the public can’t be ignored.
 
the first thing that popped into my head when i read this post earlier in the van, was harmonics. especially as the dimmer units ect may be switched mode, and i know DMX supplies use electronics. As spin mentioned, it may also be something as simple as a loose connection.
 
Thre things I'd be looking at, loose connections, undersuzed neutral conductor then un balanced phases (can we still call them phases when refering to 3 phase?).
Phases is awite as a generic term, if you refer to an individual core (allegedly) it's a line ... go figure :)
 
Seems a complex problem.

I know I do not have the experience to answer, but would like to know what happened as a learning opportunity.
So here is how I would look at the situation, please advise (have not been doing this long)

First is to check is the size of the neutral.
If someone has used the 'over half' rule and put in a tiny neutral it could be as simple as massively unbalanced lighting resolved by client education of balancing loads (or putting in a decent N).

If the neutral is equal size with conductors then my guess would be harmonics causing positive interference on the neutral conductor and ramping the current.

That would be a lot harder to fix and short of just putting a bigger neutral in I am not sure what to do.

I would like to know what the relevant current draws are on each line. a few clamp meters and get them to go through their lighting sequence seeing how it changes.

So anyone feel like helping a noob learn?
 
Seems a complex problem.I know I do not have the experience to answer, but would like to know what happened as a learning opportunity.So here is how I would look at the situation, please advise (have not been doing this long)First is to check is the size of the neutral.If someone has used the 'over half' rule and put in a tiny neutral it could be as simple as massively unbalanced lighting resolved by client education of balancing loads (or putting in a decent N).If the neutral is equal size with conductors then my guess would be harmonics causing positive interference on the neutral conductor and ramping the current.That would be a lot harder to fix and short of just putting a bigger neutral in I am not sure what to do.I would like to know what the relevant current draws are on each line. a few clamp meters and get them to go through their lighting sequence seeing how it changes.So anyone feel like helping a noob learn?
Have a look for "neutral harmonics" on Google, some of it is heavy going.
 
Hi Guys

I have been looking at the above thread to try and figure out my problem which is similar.
I work on a very big construction site and we deal with a lot of substations supplying different parts of the site.
At our main office block I have seperated our offices into smaller sections each supplied by an office DB (This is all temp electrical installations i.e. the orange boards) Today I was called out as a lot of PC's and air cons had popped! Upon opening the DB the main incoming neutral had completely burnt away as in the lugs connected onto the neutral stud were gone! I have an earth leakage relay that was protecting the secondary side but for some reason it had not operated. This is a 3 phases installation and a TN-S earth arrangement. My biggest question is why did the PC's and aircon's (220V) blow up. All that happened was that the neutral was gone therefore the circuit was incomplete and the appliances would stop working not blow up as if they were receiving 380V? Really stumped on this.
 
When you lost your neutral you effectively put 400volt across the LIVES on your single phase system, you had what is referred to as a floating neutral.

You have to remember that each phase is at 120 degrees to each other and so lags each other at a potential of 400volts. The neutral ties this down as to be Uo-230, if you lost that neutral then you are back at 400 volts.

The earth leakage will not have operated as you never had an earth fault.
 
So just to confirm even though my neutral was missing the one live wire in the single phase circuit was now carrying 400V into the socket outlets and then into the aircons etc?
 
Wow thanks so much for your help I really appreciate it as I have to give an answer to the big bosses as their PC's blew up which is never a good thing. Is there any possible solution to prevent this from happening again apart from making sure the connections are tight? Thanks again
 
How many terminations have you on site ? Terminations fail with age and load, all you can do really is introduce a good PPM system

I'm surprised that part of your insurance agreement does not insist on yearly thermal checks on your panel boards to detect hot spots.

Fluke actually do an hand held infrared thermometers that you simply point at the terminations or DB and it will detect hot spots, using this with a good PPM schedule will highlight problems before they happen

Portable Thermometers | Fluke 60 Series Handheld Infrared Thermometers
 
Have had a look at the instruments and management have agreed to buy this Fluke so as to prevent this. I am not sure what the insurance policy states as I was transfered here in July but will check that up (thanks again for that). Do you think surge arresters would have helped in this case? Just a thought? As you can probably see I have to fix up a lot of issues left behind! I know one sparky shouldn't wrong another one but one cannot help think what they were thinking
 

Reply to 3 Phase 125 a fused isolator, neutrals all melted! in the Electrician Talk | All Countries area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hope everyone has had a great Christmas and here’s hoping we all have a better new year coming our way ! Remember our riches aren’t measured by...
    • Friendly
    • Like
Replies
11
Views
564
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
760
  • Sticky
  • Article
Thanks so much for sharing this with us! I’ll definitely take a look, it seems like there are a lot of useful and interesting products. The idea...
    • Like
Replies
5
Views
2K

Similar threads

As the cable itself has had the cpc cut off at both ends I would enter a C3 as it doesn't offer any protection within the cable if accidentally...
Replies
3
Views
469
When I was on the electric board We had a pair of pillocks connect a housing estate to a very large genset, the n lead was in two parts and not...
2
Replies
28
Views
4K

Search Electricans Forums by Tags

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top