It would have depended where you fitted these SPD. They will come in 3 classes Type I II and III the type I will normally be fitted at the origin of the supply mainly for transient voltages due to lightening strikes and are not that common in the UK.

Type II would be at local distribution boards if they are 3 phase then the SPDs would not have been much use for you as the 400volt would not be deemed a surge, if they were single phase boards then yes they would have protected the system. These type are quite common in installations that have high switching due to inductive loads such as motors, elevators or HF lighting.

The Class III are very local and are often incorporated into a BS 1363 Socket outlet to protect appliances or equipment as a singular option.

These items are not cheap and it really would be a costing exercise. Personally I would be advising a good PPM schedule with the infra red technology, and perhaps even if the insurance don't insist on it having a contracting in once a year to do thermal imaging
 

Reply to 3 Phase 125 a fused isolator, neutrals all melted! in the Electrician Talk | All Countries area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
300
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
812
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
869

Similar threads

When I was on the electric board We had a pair of pillocks connect a housing estate to a very large genset, the n lead was in two parts and not...
2
Replies
28
Views
4K
Just stick the 63amp fused connector before the Henley block , or Lucy block as you call it, and your all good, as for your 2nd point, , the...
Replies
1
Views
1K

Search Electricans Forums by Tags

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top