Hi, I have been out to a property 3 times in the past week to a country pile with a 3 phase supply that keeps blowing it's 100amp distributor fuse.

The property has a pool house, a large garage with power, stables with power and a wooden annex type space also with power.

I have taken off every accessory in this huge place and can't find any obvious issues.

At the board I have measured a PFC of 1.19 kA and a PSCC of similar.

Nothing trips in the board when the dist fuse goes, I've not done a lot of work with 3 phase so unsure where to go from here.

Any advice much appreciated.
 
Hi, I have been out to a property 3 times in the past week to a country pile with a 3 phase supply that keeps blowing it's 100amp distributor fuse.

The property has a pool house, a large garage with power, stables with power and a wooden annex type space also with power.

I have taken off every accessory in this huge place and can't find any obvious issues.

At the board I have measured a PFC of 1.19 kA and a PSCC of similar.

Nothing trips in the board when the dist fuse goes, I've not done a lot of work with 3 phase so unsure where to go from here.

Any advice much appreciated.
I you have only one of the three 100 amp cut out fuses that blow, that would indicate that that phase is being overloaded. Check the balance and loads of the three phase and rebalance the 3 phase loads.
Hi, I have been out to a property 3 times in the past week to a country pile with a 3 phase supply that keeps blowing it's 100amp distributor fuse.

The property has a pool house, a large garage with power, stables with power and a wooden annex type space also with power.

I have taken off every accessory in this huge place and can't find any obvious issues.

At the board I have measured a PFC of 1.19 kA and a PSCC of similar.

Nothing trips in the board when the dist fuse goes, I've not done a lot of work with 3 phase so unsure where to go from here.

Any advice much appreciated.
The cut out fuse that keeps blowing is obviously overloaded. Check the load demand on that phase. Also, check the balance of all three phases and rebalance accordingly.
 

Reply to 3 phase domestic installation issues in the Domestic Electrician Forum area at ElectriciansForums.net

Similar Threads

Just stick the 63amp fused connector before the Henley block , or Lucy block as you call it, and your all good, as for your 2nd point, , the...
Replies
1
Views
665
  • Question
Help please, this is my first post on this subject regarding solar panel / battery installation into house with 3 phase supply. I am a DIY level...
Replies
0
Views
2K
  • Question
For anyone looking into the same thing I’ve just found a guy who did an experiment to see if this is how the 3 Phase meters counted units and it...
Replies
3
Views
1K
  • Question
so put the main CU on 1 phase, then maybe the outhouse and charger on another. then you have a spare phase to play with if loads are unbalabnced...
Replies
19
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks